Mitsubishi SOFTGOT

Ranjith

Member
Join Date
May 2007
Location
Melbourne
Posts
316
I am trying to get access to a remote site and run the HMI program on my PC.
I already can connect to the PLC (FX3) on site via an E W O N. What I want to do is now to run the HMI program on my PC and connect to the PLC on site. So the HMI running on my PC connects to the PLC on site. Is SOFTGOT is the answer? I dont have much experience with Mitsubishi. HMI on site does not not support VNC.
 
When you connect to FX3 through E W O N router your computer sees that PLC as if it is directly connected with LAN cable. You can use SoftGOT or any other solution as long is it programmed/configured in PLC. If you have already one HMI, presuming it is MC protocol, you could for example connect new one by programming PLC as Modbus TCP/IP slave.
 
When you connect to FX3 through E W O N router your computer sees that PLC as if it is directly connected with LAN cable. You can use SoftGOT or any other solution as long is it programmed/configured in PLC. If you have already one HMI, presuming it is MC protocol, you could for example connect new one by programming PLC as Modbus TCP/IP slave.

Thanks for the info.
What do you mean by "If you have already one HMI, presuming it is MC protocol, you could for example connect new one by programming PLC as Modbus TCP/IP slave".
 
There is a HMI on site GT2103-PMBDS.
But it's a very basic one.

So I would presume that it is connected through side connector (RS422/485/232) on HMI to Mini DIN connector on FX. If the PLC is not the one with built in Ethernet, that means that you need to have additional board or adapter, RS485 or Ethernet, in order to have possibility to control with other HMI.
 
So you can program FX3U, and configure for example FX3U-ENET for Modbus TCP/IP on port 502, or for MC protocol on some other port, and than you can program second HMI to access to PLC.
 

Similar Topics

Hi, Correction: title should say GTDesigner3 (not softGOT) I've updated some GUI pages using GT designer3 and I'm at the point where I want to...
Replies
9
Views
2,640
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
92
I have Toyopuc PLC PC10G-CPU and some communication modules of it. With this modules I'm able to connect with Ethernet, Ethernet/IP, FLnet, FRMT...
Replies
0
Views
52
In this sample programming, what does U4 mean? Any assistance would be greatly appreciated.
Replies
8
Views
169
Hi, I have a project with a R04CPU, RD77GF16 and a RJ71PN92 modules. The cell is given to me to change the program since the previous integrator...
Replies
2
Views
92
Back
Top Bottom