SIWAREX modules under S7-1500
Kevbo
Aug 2006
Albuquerque,NM
27
I beat my head against the wall over this one...maybe someone will find this note and it will save them some time: (maybe it will be me when I have forgotten this tidbit!)
If you are trying to access the DRs of a SIWAREX module from a S7-1500, and following the manual, you will be very frustrated, because you will be unable to read or write any values to the module itself. (you can write to the DB all day long, but you have to use the command registers in order to move the values from/to the hardware)
The S7-1500 technology object for accessing the DRs of the SIWAREX CS and FTC modules (and maybe others, I only have experience with these two flavors) has a couple of changes (vs. other processors) to the command codes:
OLD command code----------------------New command code
203...230------------------------- 2003...2030 (read from DR03...DR30)
403...430--------------------------4003...4030 (write to DR03...DR30)
605---------------------------------7001 (Read DRs 03,04,09,15 & 30)
610---------------------------------7002 (write DRs 03,04,09,15 & 30)
This is CS specific, but I recall the FTC being very similar.
This is not in the SIWAREX manual. I have seen it in an obscure note for the FTC, (which I can't find now!) and in a FAQ for the CS titled "How can a SIWAREX CS be used with a S7-1500 CPU?"
Hi All, Onboard our ship, we have anumber of cranes that are PLC controlled. One of the S7-300 modules for crane loading is of course a Siwarex...
1,867
Hello, I have a problem calibrating siwarex ms with siwatool ms Whatever I have tried, I have communication error and numerous retries to...
74
Hi We have a SIWAREX 231 weighing card controlled via PLC (not stand alone) We have used these for a while with no issues. We can auto and...
1,095
Hello, Can i use this https://mall.industry.siemens.com/mall/tr/tr/Catalog/Product/7MH4960-6AA01 with something like this...
973
Hello all, I need to know more about this module (siwarex wp231) please How to program and how can i deal with it inside TIA portal (address...
1,455