Can you help me, I am using compactlogix cpu with ILX34-MBS485 card as Rs485 master in serial modbus network to make communication wth micro850 as slave.
But I have 2 questions:
1- How can I read Multiple registers per one command although in the configuration of ILX34-MBS only you can identify one register address per command.
Ex: if i have 2 real registers to read 300001-300002 & 300003-300004.
2- Can I enable all 30 commands at one time or it will make problem?
In attachment my ILX34 Configuration to read 2 real registers per 1 command
If the registers are contiguous, as in your example, you simple increase the count of registers to read to encompass the full block.
Thanks Dravik for your reply.
if I put the first word address in configuration and I will increase no. of count.
So, I can read all the registers . Is it right?
and what about enabling all commands at one time or must toggle between commands.
Offhand I don't know re: the commands. I would pose that question to Prosoft's tech support and see what they recommend.
you should be able to read multiple addresses in a single modbus poll. There are some things in my experience that limit this though. Baud rate, serial cable length, and number of addresses being polled at once. If you have a high baud rate, long cable length, and high number of addresses being poled at once you may have issues. If you have a long cable and want to poll multiple addresses, lower your baud rate. If you need a high baud rate and have a long cable, split your number of addresses into multiple polls. etc etc. you have to find a happy balance.
sorry i cant help more with your configuration question, my comments more apply to modbus protocol experience
Hello Friends; We have 10 NOS. the machines which were designed in RSLOGIX 5000 and the control system is TT4000 by SOLAR TURBINE. I want to...
3,833
I have twelve ControlLogix controllers spread throughout an oil production facility with local Panelviews on each unit. All PLCs are connected...
3,557
Hi all, I would like to read ASCII weight from 2 scales into a single serial port on a MicroLogix 1400 using RS-485. I haven't seen any posts on...
3,103
Hi! Can anyone help me with ModBus TCP Read Multiple Registers(Function Code 03)? I have a Master Request: 00 00 00 00 00 06 01 03 64 06 00 07...
3,923
Hi all, I am writing a program where the user will input a bunch of individual registers they want to read. I am going to sort these registers...
13,666