First the AO, now the AI...
tomalbright
May 2006
Gonzales, LA
691
Not my week.
I finally got my AO going, but I have an AI with issues. This system has been online for several months. I have no idea what happened, lost an discrete output module last week, now this.
I have replaced the AI module. Getting a message in RSLogix:
(Code 16#0009 Module Configuration Rejected: Parameter Error.
Additional Fault Code 16#0001
I have reloaded the processor. no effect. Here's some screenies of the module settings:
All the channels are configured like this:
That is correct. Originally, all the AI's were 1.1, and working fine. I have 4 others that still are. I changed the rev to match the hardware to see if that made any difference.
You might try the card in a different slot, or in another rack. Just to prove the problem is with the card. We had the same problem a couple of months ago with an IA16, and the problem was the rack. After close inspection we found evidence of a short at the slot. Still not sure what caused it.
I moved the card to another slot, and configured it. Looks like it's working. I'll have to wait for some down time to change the tag aliases, though.
Thanks. This was screwy.