Question Studio Logix 5000 v.30.11 - ONS issues

Good afternoon to all.

I am running a 1769-L27ERM-QBFC1B with version 30.11 of Studio Logix 5000. I have issues with an ONS bit I have created. I have multiple parallel inputs that all tie into 1 ONS bit, which in turn, enables my output. However, about 40% of the time, the output does not come on? I am 100% positive I am resetting all inputs to off before turning any inputs back on in order to re-trigger the ONS bit.

My work around is using a pulse timer to keep on re-triggering the ONS bit until it turns my output on, but I am not sure why it will not work without the pulse timer.

What to do to troubleshoot this? I've attached my rung in the picture below.

Thanks!
Attached Images
File Type: png logic.PNG (17.6 KB, 141 views)
  Reply With Quote
Old June 27th, 2018, 03:24 PM   #2
defcon.klaxon
Lifetime Supporting Member
United States

defcon.klaxon is offline
 
Join Date: Feb 2015
Location: Far NorCal
Posts: 405
You're spot on about needing to ensure that all inputs to the ONS need to reset before the ONS will fire again, so it's good that you're taking care of that. What I would do in this situation is temporarily remove all the parallel rungs and test each one individually. If you find the ONS works for some but not all, then you have found which input is the culprit for odd behavior and you can go from there. It could be that something isn't resetting as you'd expect.
  Reply With Quote
Old June 27th, 2018, 03:34 PM   #3
fenix
Member
United States

fenix is offline
 
Join Date: Jul 2017
Location: Indiana
Posts: 21
Any reason why you don't want to give each branch its own ONS instruction?
If the drivers are not enabling a ONS in parallel, then the reset timing of the driver bits no longer mattes.
  Reply With Quote
Old June 27th, 2018, 05:12 PM   #4
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 238
It's happened on all 4 of my input conditions. I've separated each input and done each one individually with the ONS tag I have created. Actually, I have 1 tag called ONESHOT that is an array from ONESHOT.0 to ONESHOT.100 ; I'm making sure I am not using that particular ONS anywhere else in the system.

I could try Fenix's suggestion, but I don't understand why my method would not work. I have more success using OSR, but I did not want to create the extra tags necessary to use this instruction either, so I went back to ONS and tried using it again.
  Reply With Quote
Old June 27th, 2018, 05:34 PM   #5
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 238
Actually, I do not want to use Fenix's method because I am using the OTL, so I don't want to have multiple OTL's of the same output in my program. Nothing wrong with doing so,it's just my personal preference not to. The way I have it written seems most efficient to me, unless anyone else can provide a better method to write that particular rung.
  Reply With Quote
Old June 27th, 2018, 05:39 PM   #6
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,983
Quote:
Originally Posted by fenix View Post
Any reason why you don't want to give each branch its own ONS instruction?
This is what I would do. One ONS per branch and you will likely solve your problem.

Also, make absolutely sure that the address for the ONS is not used anywhere else. I normally try to make my
"OneShot" tag locally scoped to help ensure this.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 27th, 2018, 06:07 PM   #7
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 238
Right, so I've already tried using one ONS per branch, and the issue is still there. The issue existed at the very beginning when I had only 1 input, 1 ONS, and 1 output. I have since expanded to 4 inputs in parallel and had to add pulse timers on each branch to keep re-triggering the ONS until the output came on.
  Reply With Quote
Old June 27th, 2018, 06:08 PM   #8
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 238
Also, I am not using that ONS tag anywhere else in my program.
  Reply With Quote
Old June 27th, 2018, 06:15 PM   #9
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 238
Furthermore, I'm making sure the latch is not getting unlatched. Basically, this output enables my barcode reader and lets an operator scan there badge in. The only way it unlatches is if it gets a successful read in the first place. The only way it can receive a successful read is for the barcode reader to enable first. The barcode reader will not enable until my output in the picture enables.
  Reply With Quote
Old June 27th, 2018, 06:46 PM   #10
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,295
If you ZIP and post your program, folks can have a look at it.

I genuinely think there's something else you're missing in the system, whether from an attached controller or HMI, or in your logic or task execution setup, in a place you haven't looked or are misunderstanding. Carefully examine the way this Routine is executed, whether in the Continuous Task or in a Periodic Task.

Because I've participated in discovering PLC firmware bugs over the course of my career, I don't tell people that it's impossible that their problem is related to a bug.

But the basic boolean instructions in the ControlLogix have been bulletproof for 20 years. It's more likely that I'll be bitten by a rabid penguin on the subway tonight than that the ONS instruction doesn't work.
  Reply With Quote
Old June 27th, 2018, 06:51 PM   #11
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,420
Quote:
Originally Posted by alive15 View Post
Good afternoon to all.

I am running a 1769-L27ERM-QBFC1B with version 30.11 of Studio Logix 5000. I have issues with an ONS bit I have created. I have multiple parallel inputs that all tie into 1 ONS bit, which in turn, enables my output. However, about 40% of the time, the output does not come on? I am 100% positive I am resetting all inputs to off before turning any inputs back on in order to re-trigger the ONS bit.

My work around is using a pulse timer to keep on re-triggering the ONS bit until it turns my output on, but I am not sure why it will not work without the pulse timer.

What to do to troubleshoot this? I've attached my rung in the picture below.

Thanks!

Based upon what you are saying, it should work, but I would NEVER parallel multiple branches to a single one shot. You're just begging for trouble when you do that. The one shot requires a transition in order to function.
__________________
  Reply With Quote
Old June 27th, 2018, 09:01 PM   #12
Aabeck
Member
United States

Aabeck is online now
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,063
+1 on BitBucket's method.

When I have to do something like this I would make 4 separate rungs with the oneshot, each turning on a bit of it's own.

Then add a 5th rung checking if each of the one-shot bits is on and latch your output there.

This will make troubleshooting a lot easier.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old June 27th, 2018, 09:15 PM   #13
BITS N BYTES
Lifetime Supporting Member
United States

BITS N BYTES is offline
 
Join Date: Jun 2005
Location: Miami Beach
Posts: 402
Smile

Quote:
Originally Posted by Aabeck View Post
+1 on BitBucket's method.

When I have to do something like this I would make 4 separate rungs with the oneshot, each turning on a bit of it's own.

Then add a 5th rung checking if each of the one-shot bits is on and latch your output there.

This will make troubleshooting a lot easier.

+1 for Aabeck.
  Reply With Quote
Old June 27th, 2018, 09:40 PM   #14
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 429
Quote:
Originally Posted by Ken Roach View Post
Carefully examine the way this Routine is executed, whether in the Continuous Task or in a Periodic Task.
That was my first thought as well. If the logic is in a periodic task, or the bits that trigger the oneshot are in a periodic task, it's possible that there may be "missed connections" without some additional "catch and release" logic.
  Reply With Quote
Old June 27th, 2018, 10:07 PM   #15
Aabeck
Member
United States

Aabeck is online now
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,063
My $0.02 on periodic tasks:

I don't program tasks periodically, to have to see if they are being called.

I call all tasks every scan, then if it only needs to run occasionally I have the start of that task make that decision, clear any bits that need cleared, set a Skip_Bit for that task and if the task needs skipped and the Skip_Bit for it is set then I do a return.

This way if it is found later that something else needs cleared it can be done inside that task.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Studio 5000 Logix Emulate - Is this a free software with RS Logix 5000 or support ? Baker in Virginia LIVE PLC Questions And Answers 33 June 8th, 2017 02:58 PM
COUNT / ADD FUNCTION on RS LOGIX 5000 / STUDIO LOGIX alive15 LIVE PLC Questions And Answers 5 May 25th, 2016 07:49 PM
Deleting revision log in Logix / Studio 5000 .ACD file? rupej LIVE PLC Questions And Answers 2 May 3rd, 2016 06:10 PM
Studio 5000 logix Designer CliveBaker LIVE PLC Questions And Answers 2 April 11th, 2016 03:31 PM
Same "ONESHOT" in Multiple Locations skyfox LIVE PLC Questions And Answers 21 May 28th, 2007 11:33 AM


All times are GMT -5. The time now is 12:00 PM.


.