Slc 5/04

kbradray

Member
Join Date
Jan 2006
Location
Columbia
Posts
175
OK guys I have been out of the game for several years, but I am sure it will come back to me. I have a 5/04 CPU that is flakey. What is everyone using to connect to the mini round connector. In the past it used to be a PM02 cable, but I am seeking the best solution today. (USB to 5/04 round programming port)

As always you help is greatly appreciated.
Ken
 
In the past it used to be a PM02 cable, but I am seeking the best solution today. (USB to 5/04 round programming port)

Hi Ken,

The PM02 is for a MicroLogix PLC, the round mini din on a 5/04 is DH+ and you will need a 1784-U2DHP cable if you are looking for USB to that port, we sell a aftermarket version that works great and is 1/3 of the cost

If you are looking for the cheapest way just use a USB CP3 cable that will connect to the DB9 port on the 5/04

Mark
 
Thank you for the correction

I told you it had been a long time. Thank you for the correction. Which cable brand do you sell. Meanwhile I will take a quick look on your website.

Ken
 

Similar Topics

I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
38
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
62
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
91
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
91
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
74
Back
Top Bottom