Kepware OPC - Mitsubishi PLC - Archestra

mbarrett87

Member
Join Date
Dec 2012
Location
Cork
Posts
9
Hi All,

I'm using Kepware OPC server to set up communications between a Mitsubishi PLC and wonderware Application server.

Every time we deploy the OPC Client from the Archestra IDE we seem to lose some of our set points that have already been fed into the Mitsubishi PLC?

Anyone know any reason why this could be happening?
 
Gelecek OPC Controls in .NET HMI Components by OPC feature.

You can use Gelecek OPC HMI Componenets.It is very easy.You can use them with c# or VB languages. By the way You dont need to write code. Easy to write- read - subcribe by that controls.

http://www.geleceksoftware.com


You can try demo version. Each componenets are OPC Client too.
(y)
 
Solution

For future reference the problem with this is that our tags in archestra were set up as read/write tags and should have just been set as read!
 

Similar Topics

Hi, In a project I have four Progressive Pressing Machine. Each machine with different PLC like Mitsubishi 'Q00UCPU' with...
Replies
4
Views
3,028
TLDR: I try to establish the OPC communication between Kepware OPC DA Client to ABB 800xA OPC DA Server. In the Kepware OPC quick client of poll...
Replies
0
Views
848
OK, this might be simple but I always remembered when accessing rockwell "global tags" or tags at the top level you could just ignore the global...
Replies
2
Views
1,322
I have a project in which I need to automatically manage some farms. They are asking me to find a way to control some small amount of IOs from one...
Replies
2
Views
1,404
I just want to log Rockwell PLC tag data to a SQL db. Is there a preference between Kepware and Software Toolbox ? Thanks...
Replies
6
Views
1,918
Back
Top Bottom