Is it possible to message from a CompactLogix on one subnet to a SLC 5/05 on a different subnet routed through a couple of ENBTs in a ControlLogix rack?
I have years of experience setting up messaging to/from CompactLogix ethernet processors through a 1756-ENBT and out a 1756-DHRIO to SLC-5/04s and PLC5s. I am very familiar with the hardware, software, and networking but have not been able to get it working. |
![]() |
![]() |
#2 |
Member
|
Yes, if the subnet mask for both devices allow it.
Show us an example of the IP addresses and subnet masks for both devices. OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: May 2013
Location: Panhandle TX
Posts: 221
|
You can open the range devices can talk to by adjusting your subnet.
The simplest way set the 3rd octet to zero. But this causes a increase in traffic seen by that device. Say... Device 1 has a IP of 192.168.1.1 Device 1 has a Subnet of 255.255.255.0 and Device 2 has a IP of 192.168.2.1 Device 2 has a Subnet of 255.255.255.0 Devices 1 and 2 cannot talk to each other under those conditions unless you set up routing rules in your switch for it. Now another method.. Adjust Device 1's Subnet.. 255.255.0.0, Device 1 can now communicate with Device 2. Device 2 however cannot independently talk to device 1. It can respond to Device 1's requests but it cannot initiate its own. to do that you would zero that third octet on device 2. This however opens the devices to ALL traffic on the second network. You can do some advanced subnetting trickery by using other numbers, its just a bitmask. Don't zero the 2nd Octet on a 192.168.x.x IP, that gets you into public internet routable address space. If you need class A use the 10.X.X.X IP, that entire block is set aside for private networks. 192.168.X.X is mostly intended for small offices, homes, etc. 10.X.X.X for corporations that would easily exceed the capacity if a class C. Any private network can use any private IP range regardless of what the thought for it was. https://www.calculator.net/ip-subnet...it=0&x=75&y=21 |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Mar 2011
Location: IL
Posts: 2
|
First, thanks for the replies. Second, I got it working.
Topolgy: 1769-L27ERM(100.0.0.73/8) --> 1756-ENBT(100.0.0.78/8 Slot 5) --> 1756-A7 --> 1756-ENET(192.168.0.78/16 Slot 0) --> 1747-L551B(192.168.130.50/16) My problem was getting the path configured correctly; I needed the correct port number to get OUT the second ethernet module in the CLX rack. I knew that port 1 in the path would go toward the backplane but had only tried a 0 to go out the ethernet port when it should have been port 2. WRONG: 2, 100.0.0.78, 1, 0, 0, 192.168.130.50 RIGHT: 2, 100.0.0.78, 1, 0, 2, 192.168.130.50 -Graffster |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Im totally new! Please help! Tool changer PLC | mike^3 | LIVE PLC Questions And Answers | 34 | November 3rd, 2015 04:28 PM |
Limit RSLinx to a single IP address on a network adapter | EuanK | LIVE PLC Questions And Answers | 6 | January 22nd, 2010 09:22 AM |
Control logix to slc 505 message instruction failure | kentuckytech | LIVE PLC Questions And Answers | 5 | December 1st, 2008 07:08 AM |
transmitting a message on a cp340 with 3964r | anotherone | LIVE PLC Questions And Answers | 0 | November 25th, 2006 08:07 AM |
Locale message display problem RSView Studio | mulderm | LIVE PLC Questions And Answers | 16 | November 13th, 2006 07:47 AM |