Old January 11th, 2021, 07:29 PM   #16
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
Five rungs for the meat of a bi-directional SQO; it does not skip fan combinations.


As to an opinion on its clarity, I can only say that is like noses: everybody has one.


xxx.png
Attached Files
File Type: pdf four_fans_drbitboy_no_init.pdf (314.4 KB, 4 views)

Last edited by drbitboy; January 11th, 2021 at 07:32 PM.
  Reply With Quote
Old January 11th, 2021, 10:15 PM   #17
nyanpasu
Member
Canada

nyanpasu is offline
 
Join Date: Aug 2018
Location: Quebec
Posts: 39
Quote:
Originally Posted by Iandayen View Post
Yes, F1 operation happens if under 85 degrees and F2, F3, F4 are all inactive.

That's why I was thinking bit shift. 4 bits, 1000 =F1, 0100 =F2, 0010 =F3, 0001 =F4

And that works out great for shifting left.

Shifting right is where I am getting confused. If F1 is active and Temperature spikes to 100 degrees for 15 minutes, I need to shift that bit right 3 times.

Can I just write to that array instead of shifting the bit right?

Leave the BSL in place for under 85 degrees then depending on temperature could write to that array? Then use those bits to activate F1-F4 operations?
You need to buffer the BSX instruction activations so they see a transition.

Bit shifting is not a good choice for this problem. I tried to do it with BSL/BSR instructions. I haven't tested it thoroughly but I think it works. I shift a 1 in the array at the LSB when F1 needs to turn on and shift that bit to the right when the other conditions are met. This way you can use a XIC .0 to turn F1, XIC .1 to turn F2, XIC .1 OR .2 to turn on F3, etc.

I would go with a longer but more explicit sequence. I've included part of an example. It's easier to troubleshoot, easier to make additions and exceptions to and easier to read.
Attached Images
File Type: jpg onlyfans.jpg (100.9 KB, 10 views)
File Type: jpg onlyfans2.jpg (100.1 KB, 7 views)

Last edited by nyanpasu; January 11th, 2021 at 10:19 PM.
  Reply With Quote
Old January 12th, 2021, 06:51 AM   #18
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
Eight rungs ([one timer + one transition] per range) to allow logic to skip, or at least shorten, the time to transition more than one combination; this is how I interpreted Lare's post #3.

In normal operation I would expect the temperature to move slowly through each range over time and this approach should behave reasonably. However, if the temperature ever jumps* over one or more ranges, two timers for different ranges will start and complete on the same scans, and the intermediate ranges either will be skipped or be current for only one scan, so caveat emptor.

The image below shows the logic for first two fan combinations, F1 and F1.5, during the timing* before a transition from the former to the latter; the logic for F2, F3, and F4 is similar.

PDF report with the full program is also attached.

* broken sensor; manual override
** T4:1/EN is 1 and T4:1.Accum is non-zero

xxx.png
Attached Files
File Type: pdf four_fans_drbitboy_allow_skip.pdf (328.7 KB, 9 views)
  Reply With Quote
Old January 12th, 2021, 02:07 PM   #19
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,520
On ladder I would code it this way. Much easier to understand than shifting bits .


There is also maybe need to add couple extra rungs.
Controlling F1 to shut F1 down completely on certain temp?

Also maybe extra set latches for F1, F2 and F3 so that if F4 is controlled, also F1,F2 and F3 are setted on.

(This is not maybe needed as temp rising should start all fans same time even)




p.s TM13 should be also 15mins, typing error there.
Attached Images
File Type: jpg fans_temp1.jpg (96.0 KB, 19 views)
File Type: jpg fans_temp2.jpg (84.7 KB, 14 views)
  Reply With Quote
Old January 13th, 2021, 09:39 AM   #20
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 24
If you wanted to do it with one rung for each fan see attached...
(just to show the premise)

Easier if you break it out into start-up, continuation and shutdown.
Attached Images
File Type: png Fan.png (13.0 KB, 72 views)
  Reply With Quote
Old January 13th, 2021, 10:09 AM   #21
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
Sidebar: I think some of these solutions have not picked up that the OP process description has each Fn state (combination) representing the state of all four fans, i.e. "F1" is not Fan 1 on/off state alone, "F2" is not Fan 2 on/off state alone.
  Reply With Quote
Old January 13th, 2021, 10:50 AM   #22
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,798
Quote:
Originally Posted by drbitboy View Post
Sidebar: I think some of these solutions have not picked up that the OP process description has each Fn state (combination) representing the state of all four fans, i.e. "F1" is not Fan 1 on/off state alone, "F2" is not Fan 2 on/off state alone.
Yep, and in "real life" there will be things like minimum run and stop times (maybe) which can serve as anti-short cycle timers and probably fail-overs to switch up the selected pattern in the event that a fan fails to start.
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.
  Reply With Quote
Old January 13th, 2021, 12:42 PM   #23
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
One more approach with three rungs, but only 8 instructions per Fn combination; F3, F4, and the output steps are shown in the image below.


What I like about this one is that the TON rung logic is more or less visually identical to the process description, as is the TOF rung logic. Also, there are only four instructions between those algorithms that turns each combination on or off.

four_fans_drbitboy_simple.png

TL;DR

Also note that the statement
  • temperature has been above 95deg for at least 15 minutes
means the statement
  • temperature has been above 90deg for at least 15 minutes
must also be true. That, along with the bit-oriented approach to setting the index to select the current output combination, allows the logic for each transition to be self-contained and independent of the other Fn ranges, so a series of ANDed [XIO/XIC Fm_bit] instructions on the Fn rung are unnecessary.


Final note: For those who notice the incnsistency in the numbering of the timers in the PDF, timer control T5 apparently does not work on my MicroLogix 1100, so it uses T8 instead.
Attached Files
File Type: pdf four_fans_drbitboy_simple.pdf (318.4 KB, 2 views)
  Reply With Quote
Old January 13th, 2021, 03:02 PM   #24
Iandayen
Member
United States

Iandayen is offline
 
Join Date: Oct 2020
Location: Colorado Springs
Posts: 5
These have all been amazingly helpful.

I also thought about the if temp >90 for 15 minutes is also true for if temp >95 for 15 minutes as well.

I was thinking about using the enable bit on the higher temp ranges as an interlock for the lower temp ranges and as a reset for those timers.

That way if the timer for the 95 or over is active it prevents the lower temp timers from even being enabled.

This is in a large building and the temperature sensor is an ambient temperature sensor. The temp swings probably won't go from 85 to over 95 or 98 in under a 15 minute span, but the code needs to be there just in case for some odd reason it does.

I've uploaded a PDF that shows the fan operations to help a bit with the confusion.

I haven't had much time the last couple of days but looking through all your suggestions I'm sure I can find something that works, I'm hoping to be able to work on it in the next day or so and will check back here and post what I have used from your suggestions.
Attached Files
File Type: pdf Fan Operation.pdf (94.8 KB, 12 views)
  Reply With Quote
Old January 13th, 2021, 06:01 PM   #25
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
[SF-1 High] and [SF-2 Low] are always Stop, [SF-1 Low] is always Start, and some of the bits are always the same in all bands, so there are effectively only five bits that need to be controlled:
  • SF-4, SF-5 and EF-1 are always the same as each other
  • The other five have various arrangements and cannot be combined
All of that is implemented (more or less) in the attached with 10 rungs and 25 instructions. This approach requires no interlocks between the bands. In testing its behavior is consistent even when the temperature jumps over a band.


The ordering of the bands is messy because it was based on a previous iteration, where all fans were off at the nominal range (Band 2). That said, I feel the per-band logic is clear, and it would be easy to change the compares to make the inter-band sequencing more orderly.


It takes 15 minutes to change the outputs any number of bands down, which may not be consistent with the first of the statements at the end of the process specification:
  • Goes down 1 level for every 15 minutes of temperature below 85
  • Goes up 1 level for a temp rise of 5 degrees for more than 15 minutes
I assume "level" means "band."
Attached Files
File Type: zip four_fans_drbitboy_simple.zip (307.5 KB, 2 views)

Last edited by drbitboy; January 13th, 2021 at 06:12 PM.
  Reply With Quote
Old Yesterday, 09:04 AM   #26
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
Quote:
Originally Posted by Iandayen View Post
Shifting right is where I am getting confused. If F1 is active and Temperature spikes to 100 degrees for 15 minutes, I need to shift that bit right 3 times.



Btw, I think you will end up somewhere else, but there is an ugly answer to this query that will complete in one scan:


Code:
F4_15min  Bits/0
---] [--+--]/[------[BSR         ]---+----
        |           [Array  #Bits]   |
        |           [Control  ctl]   |
        |           [...         ]   |
        |                            |
        | Bits/0  ctl.EN   ctl.EN    |
        +--]/[------] [------(U)-----+
        |                            |
        +-----------[BSR         ]---+
        |           [Array  #Bits]   |
        |           [Control  ctl]   |
        |           [...         ]   |
        |                            |
        | Bits/0  ctl.EN   ctl.EN    |
        +--]/[------] [------(U)-----+
        |                            |
        +-----------[BSR         ]---+
                    [Array  #Bits]
                    [Control  ctl]
                    [...         ]
I am pretty sure the [XIO Bits/0 XIC ctl.EN OTU ctl.EN] can be simplified to [XIC Bits/0 OTE ctl.EN].



The correct answer is to assign 1 to the Bits INT, of course .
  Reply With Quote
Old Today, 05:30 AM   #27
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
I have a request for clarification from the OP.


Here is a restatement of the process behavior rules:
  1. Band 1 if temperature below 85 for 15 minutes
  2. Band 2 if temperature between 85 and 95
  3. Band 3 if temperature over 95 for more than 15 minutes
  4. Band 4 if temperature over 98 for more than 15 minutes
  5. Goes down 1 level for every 15 minutes of temperature below 85
  6. Goes up 1 level for a temp rise of 5 degrees for more than 15 minutes
Questions
  • For the 5 and 6, can we assume "level" means "band?"
  • Does rule 6, +5deg for 15min => up 1 band, makes sense if rules 1-4 are in place?
    • Say the process is in Band 2 with the temperature at 85deg. The temperature goes up 5 degrees to 90 and stays there for 15 minutes, so rule 6 says to bump the process up one band to Band 3. On the next scan, rule 3 is not satisfied, but rule 2 is, so the process drops back to Band 2 after one scan at Band 3, i.e. maybe 50ms. Is this desired behavior?
      • If not, and the process should stay in Band 3, then say the temperature goes up another 5deg to 95 and stays there for 15 minutes. Rule 6 again says to bump the process up one band to Band 4. The process is now in Band 4 at 95 degrees. How can it leave Band 4?
  • The way rules 3 and 4 are stated, and assuming the temperature does not suddenly drop below 85 from band 3 or 4 to invoke rule 5, there should be no delay for a transition from either Band 4 or Band 3 to Band 2. Because on the scan when the temperature drops from 99 or more to 98 or less, the rule 4 condition is false, and the process cannot stay in Band 4. The same logic applies to Band 3. Is that correct?
  • How does rule 5 execute?
    • Say the process is in Band 4 with the temperature at 100deg. The outside temperature could never drop 16deg in one scan to be less than 85, but say it does, as OP suggests. The process should drop to Band 3 immediately (rule 4 condition is false), but not drop from Band 3 to Band 2 for 15 minutes (rule 5, assuming temperature stays below 85), and then to Band 1 another 15 minutes after that (again rule 5). Is that correct?
    • Say the process is in Band 3 and the temperature drops to 84deg in one scan. The process should drop to Band 2 immediately (rule 3 condition is false), but not drop to Band 1 for 15minutes, which would happen anyway with the delay on rule 1. Is that correct?
  Reply With Quote
Old Today, 09:10 AM   #28
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,964
Assuming the above is correct, I modified the code to follow Rule 5 (drop one band per 15 minutes when temperature is less than 85 deg), and attach it here. It actually uses fewer instructions but is more complex.


I still don't know what to do about Rule 6.


TL;DR
  • All four temperature transitions toward, but not beyond, the Band 2 range are immediate.
    • Band 4 to 3
    • Band 4 to 2
    • Band 3 to 2
    • Band 1 to 2
  • The remaining five upward temperature transitions use the Band 3 and/or 4 TON timers and complete in 15 minutes
    • Band 1 to 3: Band 3 on timer
    • Band 1 to 4: Band 3 and 4 on timers run in parallel
    • Band 2 to 3: Band 3 on timer
    • Band 2 to 4: Band 3 and 4 on timers run in parallel
    • Band 3 to 4: Band 4 on timer
  • Rule 5 only applies to the remaining three downward temperature transitions, which all complete in 15 or 30 minutes
    • Band 2 to 1: 15 minutes Band 1 on timer
    • Band 3 to 1: immediate 3 to 2; 15 minutes 2 to 1
    • Band 4 to 1: immediate 4 to 3; 15 minutes 3 to 2; 15 minutes 2 to 1
  • As a result, a separate TOF off-delay timer is only needed for Band 3 in that one case when the temperature changes from the Band 4 range (T>98) to the Band 1 range (T<85).
    • The process leaving Band 4 is always immediate when temperature drops out of Band 4 range (T>98)
      • Immediate to Band 2 or 3 if new T>84
      • Immediate to Band 3 if new T<85
      • There is no need for a Band 4 off timer
    • The process leaving Band 1 is always immediate when temperature rises out of Band 1 range (T<85)
      • Immediate transition to Band 2
      • One or both of Band 3/4 TON on timers may start
      • There is no need for a Band 1 off timer
    • The process transition into Band 1 only ever comes from Band 2, whether previous temperature
      • was in Band 2 range (84<T<96) and Rule 5 is not in effect, or
      • was in Bands 3/4 range (T>95) and Rule 5 is in effect.
      • The Band 1 TON on-delay timer has logic to only run when T<85 AND process is in neither Band 3 nor Band 4 (i.e. AND process is in either Band 2 or Band 1,) so that Band 1 on-delay timer is in effect a proxy for a Band 2 "off delay" timer when Rule 5 is in effect.
      • There is no need for a Band 2 off timer
  • The only inconsistencies above are in the 3 to 2 process transitions, two of which are immediate and the other, where the temperature drops from the Band 4 range (T>98) to the Band 1 range (T<85), is not.
    • That choice, whether to use Band 3 off timer, is made when the temperature drops out of Band 3 range (T>95).
    • Because Band 3 is processed in the scan before Band 4, and with the assumption of either synchronous I/O and ladder scan or mapped I/O, when Rung 0004 below is scanned the [Process in Band 4] bit will be 1 if it was 1 from the previous scan
      • [XIO Band3OnTimer/DN XIC ProcessInBand4] pair at the beginning of the rung is in effect a one-shot because if Band3OnTimer/DN is 0 then not (T>95), so not (T>98) must also be true, so ProcessInBand4 will be assigned 0 on a later rung in the same scan.
    • So if
      • the process will not be in Band 3 (Band3OnTimer/DN is 0 because not T>95),
      • and the process was in Band 4 (Band 4 bit is 1),
      • and the temperature is not in the Band 1 range (GEQ N7:1 85),
    • then the transition out of Band 3 will be immediate the Band 3 off timer will not be used
      • so the Band 3 bit is unlatched to break the seal-in on Rung 0005 that maintains the effect of the Band 3 off timer, which timer starts when Band3OnTimer falls from 1 to 0.
    • Rung 0005 maintains that [Process in Band 3] bit until the off timer is complete, unless one of the following occurs.
      • If the [Process in Band 3] bit was unlatched in the previous rung, the seal-in branch is false
      • If temperature leaves the Band 1 range (not (T<85), the seal-in branch is false
      • The temperature check on the seal-in branch by itself, without Rung 0004, is not enough:
        • In the case where the temperature jumps from the Band 3 range to the Band 1 range, the process change from Band 3 should be immediate.
xxx.png
Attached Files
File Type: zip four_fans_drbitboy_rule5.zip (313.9 KB, 0 views)

Last edited by drbitboy; Today at 09:12 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RS500 Bit Shift kjacoby LIVE PLC Questions And Answers 5 February 24th, 2017 07:56 AM
micrologix bit shift khewes LIVE PLC Questions And Answers 8 May 27th, 2016 03:43 PM
installing a panelview 600 + rjmarinaro LIVE PLC Questions And Answers 10 June 17th, 2008 12:52 PM
Bit Shift Left (BSL) instruction problem - See attached code jonb452 LIVE PLC Questions And Answers 14 March 19th, 2008 09:51 AM
Moving data into a bit shift josepa LIVE PLC Questions And Answers 2 October 17th, 2006 09:37 AM


All times are GMT -5. The time now is 06:38 PM.


.