Hi Everyone,
I need help in setting up the tank level control using power flex 525 to control a pump which feeds the tank. I am planning to use the PIDE to control the level but according to my customer request he wants me to ramp the pump to fill around 60HZ (Max) speed initially until I fill the tank half (20 Litres).
My plan is to use a manual speed command to Output frequency until I reach the required setpoint keeping the PIDE disabled. once I reach the desired level I will activate the PIDE in Auto mode. This way I can have my PIDE manual mode as a fail safe entry for the operator to enter the speed directly into the PIDE CV Value.
Please let me know if you need any further info and if my scenario is correct.
Thanks in advance.
I need help in setting up the tank level control using power flex 525 to control a pump which feeds the tank. I am planning to use the PIDE to control the level but according to my customer request he wants me to ramp the pump to fill around 60HZ (Max) speed initially until I fill the tank half (20 Litres).
My plan is to use a manual speed command to Output frequency until I reach the required setpoint keeping the PIDE disabled. once I reach the desired level I will activate the PIDE in Auto mode. This way I can have my PIDE manual mode as a fail safe entry for the operator to enter the speed directly into the PIDE CV Value.
Please let me know if you need any further info and if my scenario is correct.