We are running into some issues with serial communications dropping out after a few days. When viewing the PLC hosted web page, we found the following "RX Message Error" count was increasing. Does anyone have information on this error?
Specifically, I'm trying to find out if these errors are indicative of general network issues (noise or frame impacts with messages from other devices on the network) or are specific to network issues with the PLC itself (noise or frame impacts for messages sent to/from the PLC itself).
We have good communications with the PLC for several days at a time, then suddenly the PLC stops responding to requests from the serial master device. If the PLC is power cycled, or the diagnostic counters are reset, comms return to normal (for a few more days).
Thanks for your help!
Unread March 6th, 2019, 12:33 PM   #2
GSNITZ
United States
GSNITZ is offline
GSNITZ's Avatar
SERIAL_R is an array of SERIAL_R_STRUCT types
Variable Name: i_udiRX_MessagesError
Type: UDINT
Comment: Number of frames received with detected errors (checksum, parity).
Unread March 6th, 2019, 12:35 PM   #3
GSNITZ
United States
GSNITZ is offline
GSNITZ's Avatar
RX Message Error is an evaluation of ALL frames received; includes frames from the master as well as all slave devices on the serial network.
Unread October 17th, 2019, 05:00 PM   #4
GSNITZ
United States
GSNITZ is offline
GSNITZ's Avatar
To close the loop on this, we discovered another device on the network was not adhering to the Modbus standard for a minimum time between frames requirement (also known as silent duration). We were able to log the network and determine that the delay between when the master requested data and this other slave responded was very short (between 1-5ms typically). The M258 was configured for the minimum acceptable interframe delay for the given baud rate (3ms). Any frames which were received before the silent duration timer expired were flagged as RX Message Errors. After a certain number of these errors were logged, the MBS port would stop responding. We were not able to determine why exactly the port would "lock-up" and stop responding; it may have been related to a hardware level bug in the serial port, however this is pure speculation. We resolved the issue by installing a gateway between the serial network and the M258; the gateway still flagged these fast messages as RX Errors, however the gateway itself has never stopped responding. The equipment has been operating with the fix in place for several months at this point in time without any further losses of communications.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Error message IdealDan LIVE PLC Questions And Answers 7 December 11th, 2017 08:40 AM
Modicon M258 How Do I upload Prog with USB Memory Stick? norman oliver LIVE PLC Questions And Answers 4 November 18th, 2016 07:03 AM
Modicon M258 Logic Controller pyea0001 LIVE PLC Questions And Answers 2 May 16th, 2013 11:36 AM
WinCC flexible Alarms Acknowledgement JNS LIVE PLC Questions And Answers 4 September 7th, 2010 03:04 PM
Modicon Concept 2.6 Warning Message bebecall LIVE PLC Questions And Answers 1 January 28th, 2008 08:18 AM