Change IP on 1788-ENBT flexlogix L34

Hi guys i have a flexlogix 5434 with 1788-enbt. On the processor is a sticker with IP 10.24.230.239 but i have no idea if that's correct.

I would like to change the IP on the card but the problem is i can't detect the card neither with bootp/dhcp nor on rslinx classic. Everything is running on WMware windows 7.

I tried using normal and crossover cable, changing the ip of the pc to 10.24.230.230 sub 255.255.255.0 running bootp/dhcp under XP

Appreciate any help

Last edited by Blayss; October 17th, 2019 at 02:52 PM.
  Reply With Quote
Unread October 17th, 2019, 03:04 PM   #2
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,469
I doubt you'd be able to use RSLinx to edit the 1788-ENBT IP Address; said address is defined and hard-coded within the RSL5K application running on the controller.

Your best bet would be to connect to the CPU via the controller's Serial RS232 port using a DF-1 driver and upload the application presuming, of course, you are running RSL5K of the same version as the CPU firmware level.
  Reply With Quote
Unread October 17th, 2019, 04:45 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,998
Are you sure that the IP address for a FlexLogix is defined in the RSLogix 5000 program ?

I've never seen a ControlLogix-family device that did not store the IP the TCP/IP Object, which in these controllers is physically handled by flash memory on the 1788-ENBT daughtercard. I'm 99% sure that I could take daughtercards between FlexLogix controllers and they would retain their IP addresses.

You should be able to "browse" through the serial port to the ENBT, and read the IP address from it.

Or, connect with Wireshark directly to the controller and cycle power, and look for an ARP packet from the 1788-ENBT that indicates what its IP address is.
  Reply With Quote
Unread October 17th, 2019, 05:16 PM   #4
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,469
Ken, he's probably on the wrong subnet. 1788s were a PITA and I had always set addresses when serially connected to the CPU. The addresses are part of the application.
Attached Images
File Type: png FXLX.png (51.1 KB, 23 views)
  Reply With Quote
Unread October 17th, 2019, 05:32 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,998
All Ethernet modules have that field in the General tab; it doesn't really do anything except allow RSLogix 5000 to exclude that IP address from the available ones for devices in the I/O tree.

In modern (I'm looking at v20) revisions of RSLogix 5000, there's also a tab labeled Internet Protocol for the ENBT module. That has a "Set" button that allows you to actually change the IP address settings for that module.

The FlexLogix is a decade or more out of date, so there could be something squirrely that I'm missing.

I definitely agree that drilling down from the DF1 serial port is the easiest way to configure, or learn the configuration of, the 1788-ENBT daughtercard.
  Reply With Quote
Unread October 17th, 2019, 06:09 PM   #6
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,469
Actually Ken, the Network Configuration tab of tbe Module Definition tab will set the IP Address of the 1788 and will retain the 'greyed-out' values of the settings wnen Offline; I had always made a point of documenting the Flex ENBTs within the applications even if not required but for IO comms.

He will need to DF1 connect and, hopefully, the EDS database will contain the 1788 file; not sure if he could use Linx to change the IP Address though. Online RSL5K had never failed at this task.
  Reply With Quote
Unread October 17th, 2019, 06:11 PM   #7
Blayss
Member
Slovakia

Blayss is offline
 
Join Date: Oct 2019
Location: Slovakia
Posts: 2
thanks guys i will try to get my hands on some serial connector
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How do you change IP Addresses on Compactlogix when your network ideas change ? Cydog LIVE PLC Questions And Answers 3 June 11th, 2018 10:56 AM
Change PowerFlex 525 IP Address xC0MMAND0x LIVE PLC Questions And Answers 3 October 23rd, 2017 05:02 AM
SLC 5/05 to PV+ IP Address Change kbradray LIVE PLC Questions And Answers 4 November 5th, 2007 05:33 PM
IT policy, I can't change my IP address on my laptop. TConnolly LIVE PLC Questions And Answers 25 July 4th, 2007 04:26 PM
IP Quick change software R_C LIVE PLC Questions And Answers 11 August 31st, 2006 07:26 AM


All times are GMT -5. The time now is 08:34 AM.


.