Looking at quoting a system with a 100hp motor for offshore use. Motor is only used a few times a month.

I’m thinking I might need to put heaters in the motor prevent condensation build up. Is this right? Is it overkill?

Spec only said 40C ambient so I’m guessing near the equator most of the time.

Thanks
 
As far as heaters go, if it is VFD controlled some VFD's have a DC standby current to keep the windings warm when the motor is off.

Plus, don't think 'condensation' - as 'humidity' can cause just as much of a problem with the temperatures too high for normal condensation to occur.
 
If there is no VFD involved, There are stand-alone Motor Winding Heaters that can be added to the motor starter to accomplish the same thing; trickling low current into the motor to keep it warm. Their main purpose is for marine motor applications. The advantage over a strip heater on the motor is that it doesn’t need a separate power source and separate wiring/conduit/circuit protection.

And if you know for sure it’s going to the tropics, you will want the “tropicalization” option to help prevent fungus damage. Most major motor mfrs offer that.
 
Last edited:
The first thing i would do is contact the motor manufactures ( Not the distributor ) and talk to their application engineer they would be the best people to advise you
Different manufactures may have different abilities
My thinking is you will need a winding heater of some type
Another thought if this is truly a remote location and not accessed often then how you deal with power outages.
 

Similar Topics

Good day everyone, Single phase motor,3/4 Hp, capacitor start, dual voltage wired for 115VAC with Allen Bradley reversing contactors and 10...
Replies
9
Views
3,047
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
112
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
323
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
Replies
2
Views
194
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
942
Back
Top Bottom