Step 7 and wincc flex dealing with timer preset help

Jeff23spl

Member
Join Date
Jan 2010
Location
Canada
Posts
860
Hello

I usually represent all my time delay in 0.001sec inside the hmi but know i need to enter values ranging to 2o minutes meaning 1200 000ms!!!

I'm using S5time variable and equivalent timer tags on winccflex for timer preset values

Do someone know a better way of doing this to fix or choose the timer preset base units
 
Use the IEC Timeers instead of the S5T timers, they take their input directly in ms and you don't need to worry about BCD or range coding which makes them much easier to feed (more or less) directly from the HMI.
 