Micrologix IO cards Error

Holmux

Lifetime Supporting Member
Join Date
Oct 2013
Location
Aalborg
Posts
279
Hi

I have a Micrologix 1400 with some external IO cards, the costumer complains about failing IO cards, especially the Analog Output card is replaced often (once every 18 months) I haven't worked that much with the Micrologix, so I don't know if there is any special things to look for.

Temperature and external power supply looks OK

Are the Micrologix external IO especially sensitive ?

Any input would be great

Thanks
/Holmux
 
They're generally pretty reliable but they do fail now and then. Like after 10 years or so. If he's got consistently failing cards I would check to make sure there's not some terrible noise or 240VAC riding on the DC bus or some other shenanigans.
 
I think you are right, I am also leaning against quality a power source problem.

Well I have been looking a bit on the setup, there is a lot of static electricity going around in the operation, so I will start with measuring the quality of the power and ground going true this cabinet.

That means I will need to go and get me some new tools, I have been looking for an excuse to get my self a portable oscilloscope for a long time, Christmas came early this year :)
 
We had a couple panels where analog input values and output levels would randomly freeze until a power cycle. The Flex IO racks were mounted to aluminum rail. None of the ground tabs on the module bases or the ASB pierced the oxide layer on the rail to actually be grounded. A switch to steel rail resolved the problem.
 

Similar Topics

I am trying to 'standardize' several HVAC units running micrologix 1400. My question: Can I 'leave out' IO cards in the IO map below or do I...
Replies
4
Views
1,506
Hey Everyone, We have a Micrologix 1400 (1766-L32BXB) with a Panelview 800 7" Screen, the Micrologix also has a 1762-IQ16 Input Card and a...
Replies
2
Views
1,284
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
22
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
40
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
Replies
4
Views
75
Back
Top Bottom