Location
oregon
Posts
8
I am upgrading four SLC 5/01 to SLC 5/04 and SLC 5/05. I didn’t have problem changing the program from SLC 5/01 to SLC 5/04. I am having problem with SLC 5/05. I am using MCP03 cable (RS232) cable and I have only one serial port on my Computer. I am having problem with RSLinx to configure the SLC 5/05.

The FLT (SLC 5/05 CPU) light is flashing

I am using RS23 DF1 communication protocol

I am using RSLinx 2.20.01,

What could be that I am missing?

thanks feo help
 
Hello tafenegus.

The serial port in an SLC5/05 is just like the serial port in an SLC5/04. So it should be possible to go online with what you have.
Are you sure that that the problem isnt with RSLogix 500 ? If your RSLinx 2.20.01 is current with your RSLogix version, then it is a bit old. Maybe the SLC5/05's firmware is too recent.

Try to reset the SLC5/05 to factory defaults (= remove battery, short capacitor).
Then try to use the DF1 autoconfigure function in RSLinx.
 

Similar Topics

Machine has existing DN devices that are connected to SLC 5/04. All communication is working fine now. Supplier wants to remove some DN devices...
Replies
6
Views
812
Hello everyone, I am migrating a program from STL to SCL via S7-1200 portal, I would like you to help me by converting these lines of code...
Replies
4
Views
1,607
Hello Everyone, I'm a pretty green PLC tech and I need help logging on to some SLC 5/04 PLCs. I have a 1747-UIC and 1747-CP3 cables and I'm using...
Replies
16
Views
6,922
Hello, I have a SLC 5/04 processor that I can't get online with and hope someone can help me with any ideas. This processor has a DH+ and DH-485...
Replies
8
Views
3,209
I've got a guy looking for help with a SLC 5/02 with a flashing fault light near Charlottesville VA. It will be a while before I can get to it...
Replies
0
Views
1,350
Back
Top Bottom