Good Morning ,

We have a shelf of ControlLogix and Compactlogix CPU's . I would like to test these and also use these for training . Can you download a program to them , same processor in the program application as what I would be trying,
without I/O ? Explained another way , just plug it in a empty rack , and download the program .

Thanks for your help ,
 
Yes, you can. The only stipulation is that the processor be in the same slot in the rack as the program calls for.

For best results, go into each I/O module's configuration, and on the <Connection> tab check the "Inhibit Module" box. Now the processor won't try to scan those I/O non-existent I/O modules, and you can write (by hand or programmaticly) any value you want to the Input addresses to simulate a response.

I personally prefer to simulate by writing to the raw input addresses ("Local:3:I.x") rather than having two separate "mapping" routines -- one for real I/O and one for simulated. YMMV.

Have fun!
 

Similar Topics

Hi Guys, Can ControlLogix with Modsim32 for Modbus Server Testing? I have ControlLogix via Anybus Modbus TCP and I need to Test the...
Replies
6
Views
249
Hello all, looking for ideas on getting some basic training done, I need to practice on maintenance timers and bypass switches (with a Factory...
Replies
5
Views
1,275
I have a project in FTV ME (Studio v13) that I'm trying to apply security to a few buttons/setpoints. I have 4 users: Anonymous Logon, DEFAULT...
Replies
1
Views
764
I have a customer asking me to do some testing on non Rockwell I/O. They want to see if it will work. Thats simple hookup a PLC, put the IO in the...
Replies
4
Views
1,093
Hi, I’m just after a couple of pointers on testing comms between SLC PLCs in a test environment (i.e. not on a live plant). For a typical...
Replies
5
Views
2,718
Back
Top Bottom