Connection Problem with Factory Talk View Studio Version 7 with compact Logic L30ER

khaiseng82

Member
Join Date
May 2013
Location
AMK
Posts
5
Dear all,

I am trying to connect Factory Talk View version 7 with compact Logic ,
My Rslinx connection is ok, but when i open the communication section "RsLinx Entreprice "--"" communication Setup"" at the factory talk view and try to create a new connection . It prompt me a window stating ""Failed to read Default Template""


Could anyone here kindly tell me what is the problem about my communication:wish:


thank you
 
What Operating System is it running on?

One possibility...

In Windows XP the Default Template is stored in the C:\Documents and Settings\All Users\Application Data\ folder.

In Windows 7 the Default Template is stored in the C:\Users\Public\AppData\ folder

Or

C:\Users\{Username}\AppData\ folder.

This is a protected folder. A User must have read/write permissions for this folder. Your logged on Windows User Account should have Administrator Privileges.

G.
 

Similar Topics

Hello 1st post so sorry if i am in the wrong place I am trying to connect to a machine running Insql 8. I add the server info in the server...
Replies
3
Views
5,394
Hello, I have an MVI56-MNET module, which is installed together with EN2TR, with a subnet of ~10, all instructions have been added to the project...
Replies
4
Views
416
Hi, I bought a Weinview/Weintek MT8071ip HMI and an EasyAccess Activation Card. I have activated the card on the HMI (it says activated), but...
Replies
1
Views
885
Hi all, I really need some advice for establishing communication between 1770 KFD with DeviceNet and my laptop. 1. What cable should I use to...
Replies
12
Views
2,412
Hello there. I have bougth a SMC EX260 SEN-1 ethernet/ip slave and i want to control it from windows PC (with Modbus TCP may be?). Is it possible...
Replies
1
Views
981
Back
Top Bottom