Power Factor Correction Capacitors

Hello,

I was just curious if a PF correction capacitor is ever used with a VFD install?

Have any of you ever needed to add a PF correction capacitor in any of your builds?



Thank you!
  Reply With Quote
Old March 9th, 2018, 10:37 AM   #2
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 763
No.

No.
  Reply With Quote
Old March 9th, 2018, 10:39 AM   #3
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,890
VFDs generally have an inherent high power factor, and there is no advantage to adding capacitors.
  Reply With Quote
Old March 9th, 2018, 11:38 AM   #4
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 763
Perhaps a line reactor to smooth out harmonic currents?
  Reply With Quote
Old March 9th, 2018, 11:53 AM   #5
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,221
I use line reactors; the few times I've been bit by not using them was enough for me to make it standard.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old March 9th, 2018, 04:44 PM   #6
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,520
Quote:
Originally Posted by Tom Jenkins View Post
VFDs generally have an inherent high power factor, and there is no advantage to adding capacitors.
Not only that but when there are VFDs, adding PFC capacitors can actually CAUSE more problems that you otherwise wouldn't have had.
  Reply With Quote
Old March 9th, 2018, 04:52 PM   #7
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 633
Quote:
Originally Posted by jstolaruk View Post
I use line reactors; the few times I've been bit by not using them was enough for me to make it standard.

Out of pure interest, how were you 'bit'?
  Reply With Quote
Old March 10th, 2018, 05:54 AM   #8
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,221
Quote:
Originally Posted by janner_10 View Post
Out of pure interest, how were you 'bit'?
On one occasion, I was commissioning a panel with a handful of VFDs and a couple of servos. The servo motion would occasionally act erratic. After much time scratching heads and thinking that it was a tuning problem, I noticed the h/w designer had not designed in line reactors for the VFDs or Servos. I asked the electrician to rummage in their bone yard and install some in the new panel and the erratic behavior disappeared (or never again showed up).
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old March 12th, 2018, 09:55 PM   #9
2rlp
Member
India

2rlp is offline
 
2rlp's Avatar
 
Join Date: Sep 2006
Location: Mumbai
Posts: 102
What's the difference between using Input reactors v/s Output reactors?
  Reply With Quote
Old March 13th, 2018, 12:10 AM   #10
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 267
Input reactors stop drive noise from contaminating the supply.
Output reactor reduce the noise on the motor cable and reduce the chance of crosstalk to other cables.
  Reply With Quote
Old March 13th, 2018, 04:57 PM   #11
snowbanx
Member
Canada

snowbanx is offline
 
Join Date: Apr 2009
Location: Saskatchewan, Canada
Posts: 1
PFC is not needed with a VFD. With a large amount of VFD's in an industrial plant, you may need to look at a harmonic filter.

As stated above, input reactors mitigate some of the noise and harmonics that are sent on the line feeding the VFD. Output reactors are to smooth out the pulsed voltage that is created from the SCR's firing. They are also used to stop the reflected voltage spikes that are created with long leads from the VFD to the motor.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Seimens S7-200 history log after power loss Alac LIVE PLC Questions And Answers 4 April 7th, 2016 03:13 AM
How to control the value of I/O device Gimac_II by Vijeo Citect? vudvpro LIVE PLC Questions And Answers 0 February 24th, 2012 09:15 PM
Merger External & internal power for Gas Detector geragai LIVE PLC Questions And Answers 4 February 11th, 2012 06:58 PM
AB 1794-L34 PLC execution time nqn827 LIVE PLC Questions And Answers 6 December 21st, 2009 03:34 PM
Common 0V only on 2 x 24VDC power supplies qwsoftware LIVE PLC Questions And Answers 7 December 14th, 2009 07:45 PM


All times are GMT -5. The time now is 12:03 PM.


.