plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old March 13th, 2018, 05:28 AM   #1
theripley
Philippines
theripley is offline
theripley's Avatar
OT: Star-Delta
Hi.
For a 100 hp (at 230 Vac) FLC is 248A (based on NEC table), is this correct:
1.) Branch circuit protection will be 248A x 250% = 620 A or 600 AT
2.) Main contactor is 248A x 58% = 145A, and main contactor = delta contactor = overload protection
3.) Star contactor is 248A x 33% = 85A
4.) Branch conductor size is 60mm2 (00 AWG). Ampacity of 60mm2 is 170A, this is > 145A.
Did I forget something? Please respond.
__________________
"Complacency is the enemy of greatness"
Old March 13th, 2018, 06:24 AM   #2
lfe
France
lfe is offline
I never chose the contactors or the delta-star starter according to the intensity. I choose the contactor according to the manufacturer's catalog and selecting the immediate superior for the motor power and voltage
One example : https://www.schneider-electric.com/e...on-and-control
This would seem the exact model for 100HP and three-phase at 230V, but if you want more margin maybe it would be better to choose the next higher
The same applies for the circuit breaker, choose one suitable for motor protection according to the power and voltage.
__________________
Suppanel HMI
Old March 13th, 2018, 08:45 AM   #3
T Gibbs
United States
T Gibbs is offline
Branch circuit conductors have to be able to carry 310 amps (248 x 125%)
Old March 13th, 2018, 07:32 PM   #4
theripley
Philippines
theripley's Avatar
Quote:
Hi T Gibbs,
I have attached herewith my diagram. I use 2 sets of 60mm2 as my branch conductor, is this correct?
As for the contactor, I will choose 1 size higher than my computation for safety.
__________________
Old March 13th, 2018, 07:39 PM   #5
T Gibbs
United States
T Gibbs is offline
I’m not sure what 60mm is in AWG. If 60mm2 wire is good for 155 amps or more then you’re good.
Old March 13th, 2018, 08:36 PM   #6
theripley
Philippines
theripley's Avatar
Just wondering, what is the implication if I use 2 sets of 150mm2 wire (295A) instead of 2 sets of 60mm2 (170A)? Aside from cost concern of course.
I was asking because we have stock of 150mm2 wire from previous project, just wondering if I can use it or not.
Thanks.
__________________
Old March 13th, 2018, 08:52 PM   #7
jraef
United States
jraef is offline
jraef's Avatar
Thanks.
For those of us in North America, 150mm2 is roughly equivalent to 300MCM, 60mm2 is roughly equivalent to 1/0 (1/0 is 55mm2).
The only potential problem with running cable that is larger that necessary is that it will not fit in the lugs of the devices made for lower currents.
To your first post:
Yes, the MAXIMUM circuit breaker could be 248 x 250%, but because it is a Reduced Voltage Starter, you could likely get away with smaller. I've done plenty of that size using a 400A breaker, never had a problem with it.
The two main contactors should be the same, and yes, 58% of the motor FLA. The Star contactor is sized to 33% of FLA minimum, but also it must be capable of being mechanically interlocked with the Start contactor (M2 in your diagram), which sometimes dictates the minimum size. You have to make sure of that before buying.
Side note: I stopped messing with all of that years ago and just use Solid State Soft Starters. No muss, no fuss, nothing to remember.
Old March 13th, 2018, 09:05 PM   #8
theripley
Philippines
theripley's Avatar
To your first post:
Hi jraef,
Your side note is the best. I learned my lesson now, thank you very much.
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Simocode Star Delta switchover problem. swapnil.naik LIVE PLC Questions And Answers 1 December 21st, 2013 01:31 AM
a star delta ladder diagram engr_shafi2002 LIVE PLC Questions And Answers 6 April 17th, 2013 07:29 PM
Star Delta Starter? mosama LIVE PLC Questions And Answers 6 September 6th, 2010 10:33 AM
OT Wye delta transformer 30 degree phase shift - why leitmotif LIVE PLC Questions And Answers 10 May 25th, 2009 10:02 PM
STAR DELTA 3 PHASE MOTOR PERSPOLIS LIVE PLC Questions And Answers 4 December 30th, 2002 09:22 AM