Old March 13th, 2018, 12:39 PM   #1
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
GE RX3i - Inputs must be retentive?

Why does GE RX3i insist that the inputs (%I) be retentive?
I edited the variable declaration table for all the inputs to be non-retentive. It loaded without fault....THEN.... when I did a "Validate" it changed all of them back to Retentive??
Error on each input said that the "Memory Area Must Be Retentive changing to Retentive"??

Why would inputs have to be retentive??
Some %I references I use in my logic may not be directly connected to input module.

I guess I will have to use a first scan bit to set all my %I bits to "0"?
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; March 13th, 2018 at 12:43 PM.
  Reply With Quote
Old March 13th, 2018, 01:05 PM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,534
The only discrete memory type where you have the choice of being retentive or non-retentive is %M memory. %T memory cannot be retentive. You could use that instead of %I for those variables in your application or else just use %M and declare the variables you are concerned with as non-retentive.
  Reply With Quote
Old March 13th, 2018, 03:28 PM   #3
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Quote:
Originally Posted by Steve Bailey View Post
The only discrete memory type where you have the choice of being retentive or non-retentive is %M memory. %T memory cannot be retentive. You could use that instead of %I for those variables in your application or else just use %M and declare the variables you are concerned with as non-retentive.
The issue here is how I do my I/O mapping. all my internal plc logic is done using high %I above 200 and %Q above 200. So I map %I0001 from PLC Input module to %I201 in logic.
This allows me to do retrofits (which I do a lot of) and new logic edits quickly using the map, without having to change everywhere the bit is used in logic.
When I am troubleshooting and See a %I or %Q, I know it is related to the real world map.
Understand?
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; March 13th, 2018 at 03:35 PM.
  Reply With Quote
Old March 13th, 2018, 04:06 PM   #4
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,534
Then what is the problem with %I memory being retentive? Presumably you run your mapping routine at the beginning of the _MAIN program so you have the latest updates from the modules every program scan.
  Reply With Quote
Old March 13th, 2018, 04:21 PM   #5
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Quote:
Originally Posted by Steve Bailey View Post
Then what is the problem with %I memory being retentive? Presumably you run your mapping routine at the beginning of the _MAIN program so you have the latest updates from the modules every program scan.
The problem is now I am doing a job that has me mapping from High to low.
I started my rack at %I0201 and am mapping down (ie...%I201 mapped to %I0001).
In my logic I may still have bits that are not mapped to (Like %I0051) and I want them to be turned off till I find them. I do not want them to come on energized...
Actually this would also exist if I mapped up. If I have not mapped %I0051, I do not want it be on.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old March 13th, 2018, 04:23 PM   #6
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
I guess I could run a "Bit Set" (or "Bit-Clear"?) in logic to set all the %I and %Q to "0" on first scan...
Once it is done I should not really have to even run it again..
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old March 13th, 2018, 04:26 PM   #7
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,534
Map to a symbolic Boolean variable instead of to a %I address.
  Reply With Quote
Old March 13th, 2018, 05:01 PM   #8
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Now I have another issue see new new post on RX3i Invalid Sweep Mode?...
Found that problem..
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; March 13th, 2018 at 05:10 PM.
  Reply With Quote
Old March 13th, 2018, 05:12 PM   #9
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Quote:
Originally Posted by Steve Bailey View Post
Map to a symbolic Boolean variable instead of to a %I address.
How about an example of how this is done?
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old March 13th, 2018, 05:39 PM   #10
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
All of a sudden..
How come I cannot edit in logic online or offline??

Fixed that by restarting Machine Edition....weird...

This has now happened 3 times. I have to keep restarting Machine edition to edit the logic??
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; March 13th, 2018 at 06:26 PM.
  Reply With Quote
Old March 13th, 2018, 06:09 PM   #11
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,534
Here is a quick example for a single variable.
The Boolean variable named "I00018" is addressed to %I18 and is retentive.
The Boolean variable named "I00019" is not addressed (Symbolic) and has been configured a non-retentive.
The MOVE_BOOL instruction copies one to the other.
Attached Files
File Type: docx Example for Nathan.docx (108.9 KB, 9 views)
  Reply With Quote
Old March 13th, 2018, 08:19 PM   #12
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Quote:
Originally Posted by Steve Bailey View Post
Here is a quick example for a single variable.
The Boolean variable named "I00018" is addressed to %I18 and is retentive.
The Boolean variable named "I00019" is not addressed (Symbolic) and has been configured a non-retentive.
The MOVE_BOOL instruction copies one to the other.
Got it! That is easy enough.
So it is using memory only for addressing and not IO addresses?
And it CAN BE retentive also, you would think that because it is memory based that it is not retentive?
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old March 14th, 2018, 08:19 AM   #13
Sapper307
Member
United States

Sapper307 is offline
 
Join Date: Nov 2017
Location: Maryland
Posts: 90
Quote:
Originally Posted by NetNathan View Post
Got it! That is easy enough.
So it is using memory only for addressing and not IO addresses?
And it CAN BE retentive also, you would think that because it is memory based that it is not retentive?
Symbolic variables have no reference address, they are easy to spot in the ladder because they are displayed in a darker shade of blue. GFK-2950 has a good description on retentiveness, transitions, and overrides in section 3. Also, personally i don't like mapping registers to registers of a similar type IE %I to %I. I would map %I to %M, then execute logic with the %M register (%M can be non-retentive i think off the top of my head). Similarly to the way you would handle %AI. You'd take a raw %AI 0-32000 count value, scale it in logic into an %R, then use the %R in logic. Use the software based registers for software based stuff and leave the real IO register types free for real IO. My 2 cents
  Reply With Quote
Old March 14th, 2018, 09:26 AM   #14
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,403
Quote:
Originally Posted by Sapper307 View Post
Use the software based registers for software based stuff and leave the real IO register types free for real IO. My 2 cents
I agree wholeheartedly. I prefer to avoid having an HMI access real IO altogether. There is no need for it in a well designed control system.
__________________
  Reply With Quote
Old March 14th, 2018, 10:20 AM   #15
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,441
Like I said...
I like mapping my %I and %Q to a higher %I or %Q.
My %AI and %AQ are moved to registers, but there are only about 24 %AI and 5-8 %AQ to deal with here....but Inputs and Outputs may approach 64 inputs and 42 Outputs.
As I am troubleshooting my logic when I see a %I or %Q I know it is related to real IO. I would have to do a search to find out if the %M is related to a %I or %Q (I could shove it into the description, which makes it even longer).
I also use the mapped address, if needed, in my Intouch HMI.
Then when I do a conversion I hardly ever have to edit anything in logic.... just my mapping subroutines. No need to change core logic or HMI.
I do a lot of conversions on other pieces of equipment... made by others, so the IO is not always in the same location as equipment my company makes, especially if the PLC type changes. The vacuum furnaces I work on have almost the same operating procedure and components.
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; March 14th, 2018 at 10:28 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GE RX3i Profinet cegomez1 LIVE PLC Questions And Answers 0 July 19th, 2017 11:02 AM
I forgot the password of the controller (RX3I / GE FANUC)!! HAJJSAID99 LIVE PLC Questions And Answers 5 July 19th, 2017 06:29 AM
GE RX3i wilsonzhu LIVE PLC Questions And Answers 1 November 15th, 2011 01:11 PM
Quick PAnel communications to GE Rx3i PLC MadPLC LIVE PLC Questions And Answers 11 September 16th, 2011 03:31 PM
Remote Racks in GE Rx3i steelman LIVE PLC Questions And Answers 2 August 1st, 2011 12:46 PM


All times are GMT -5. The time now is 12:11 PM.


.