Thanks all for the suggestions/advice.
Some further testing revealed that the valves are not AS-I ready, so I am leaning towards a discrete I/O solution. It is possible that we will replace the valve head and controls, depending on if the how many valves' current electronics are functional, at which point I'll revisit the AS-I option. I do personally think this would be the cleanest solution with the least wiring. Fortunately, the complexity of the install was not lost on management, so I have some additional planning time for the project.
That said, for the discrete I/O I am leaning towards POINT for the following reasons informed by the info provided here:
-Compatibility with 1756
-Personal familiarity
-Uniformity with the rest of the facility
-Smaller footprint than compact i/o
-Lower cost
-I have settled on using POINT IO for the tanks
I will need 90 modules total, not including spares. I have not used the extension cables before, and have some questions. I tried looking it up for myself, but the only description I found was on page 49 of the selection guide.
-Even with the cable, the module limit for one AENTR is 63 modules?
-The cable only serves as a means of organizing, it does not change the functionality, correct? E.g. 40 modules on one AENTR is equivalent to 20 modules on an AENTR with another 20 on the extension cable?
-Are the power requirements different due to the cable run, or am I overthinking this?
I will do some rack length calculations today. We have a 60" by 36" enclosure that we would like to use for this, but cramming all the wiring into one space might be the limiting factor here. Perhaps multiple panels as others suggested will be necessary.