Hello- 1st off - I don't get involved with many Siemens PLC's here
I have a 231-4HD32-0XB0 4 channel analog in and a customer provided program.
The customer used a "limit" function to keep the raw analog in between 5530 and 27648 before he normalizes it.
In the device configuration, he has the modules set up as 4-20mA. If the module was configured as 4-20mA wouldn't the range be 0-27648? Or is the raw always 0-27648 for either 0/20 4/20mA and you compensate by setting your min normalized or scaled value to 5530?
Thanks.
I have a 231-4HD32-0XB0 4 channel analog in and a customer provided program.
The customer used a "limit" function to keep the raw analog in between 5530 and 27648 before he normalizes it.
In the device configuration, he has the modules set up as 4-20mA. If the module was configured as 4-20mA wouldn't the range be 0-27648? Or is the raw always 0-27648 for either 0/20 4/20mA and you compensate by setting your min normalized or scaled value to 5530?