Short of cycling power, what might cause a PLC-5 (5/20C) to lose its IP address?

I know on power up, the PLC must query the BootP server to get its IP address. Is there anything else?

We had a PLC lose its address this afternoon during a power sag (about 1 second). Our system is set up so that the PLC should never have seen this sag - it is on a UPS that should have kept power to it for almost 30 minutes! Despite the UPS, I suddenly had no Ethernet communication with this PLC, and I had to restart the BootP server to fix it (long story why that wasn't running . . . )

We will certainly be verifying the operation of the UPS the next time the line is down, but in the meantime if anyone has any thoughts, I would appreciate hearing from you.

Thanks,

Marc
 
Did the PLC-5 keep it's program during the loss of the IP address, and is the battery good ?

I think the PLC-5's action is an indication that your UPS didn't function as desired.

The only time I've seen 1785-ENET (because you said it's a 5/20C I assume that's what you're using) go to BootP mode unintentionally was a system on which the IT department decided to enforce IP address leases and send a "Force Renew" command to every BOOTP/DHCP client that had been using it's IP address for more than 7 days. The PLC-5 dutifully renewed it's IP address with the BOOTP server... and joined the office IP domain, rendering it mute to the production subnet.
 
Check to see that the UPS is an online type. If it is an offline type, there will be a momentary changeover time before going to battery. Also check that the UPS batteries have been discharge tested regularly. They do gain a memory sometimes and can also be failing if not regularly tested.
I have seen this type of event before in a power station where the PLCs momentarily dropped offline when the UPS changed over. The PLCs were SLC500s. In this case it caused a blackout.
beerchug
 
Thanks to you both for the replies. My guess was the UPS - I just wanted to see if there was anything else that might be the cause.


Ken - in answer to your questions:

Yes, we are using the sidecar 1785-ENET.

Yes, the battery is good. We change them regularly, and tested this one fairly recently. The BATT diagnostic light was not illuminated.

Yes, the PLC retained its program - simply restarting the BootP server and cycling power to the PLC was all I did to restore normal operation.

The PLC is on a separate control network with 4 other PLC's and a SCADA node - nothing else (so there wasn't a "Forced Renew"). We are reconfiguring portions of this line, and this is the only PLC that has not been updated to disable BootP (so the fact that ONLY this PLC lost its address isn't significant).

Thanks again for the replies,

Marc
 

Similar Topics

I am working with beckhoff plc in twincat 3 environment. I have a array of struct which I want to make persistent. I declared it with...
Replies
0
Views
97
Good Morning All, I have a Siemens 6ES5 466 PLC. We are intermittently losing parameters . We can pull the backup battery and power down. When...
Replies
2
Views
1,185
Have a PLC5/40E that has a battery installed and a working battery warning light that is off with the battery plugged in. There is no memory...
Replies
8
Views
2,640
I am using a LS PLC - DR60SU - to control various control loops. I have set up the PID loops in the PLC and am using an HMI to set the sepoints...
Replies
0
Views
3,410
Hoping to catch a seasoned guru's attention on this thread who knows these drives. We have 3 PowerFlex 700s controlling fan motors in a cooling...
Replies
28
Views
9,642
Back
Top Bottom