Downloading to a 300 Micro Panelview

Coachman

Member
Join Date
Sep 2006
Location
Maryland
Posts
97
Having a difficult time downloading a application to a 300 Micro
Panelview. It does not recognize the Panelview. What procedure would you recommended to download to this Panelview. I am using
a 1761-CBL-PM02.

Thanks in advance



 
There are 2 ways to download.
1) Using the point-point DF1 driver installed with the Panelbuilder32 software.
2) RSlinx, using the DF1 driver.

What method is not functioning?
A problem that I have run into is that if you already have PV+ Com 1 driver running, there will be a conflict with the port.
Another is that you have RSLINX running as a service, with a DF1 driver ready. This will conflict if you are using the built in driver in Panelbuilder32.

Let us know a little more about your issue,.
 
With your micro 300 connected to your PC;
Open RS Linx.
select communications
select configure drivers
select configure
select auto configure

That should recognize your panel view and make you good to go.
 
I'm going to propose a new Forum Law for 2007:

"No Allen-Bradley PanelView questions shall be answered unless accompanied by the complete part number of the PanelView terminal."

This Forum Law shall not supplant nor modify the Commandments, including "thou shalt include precise error message text", and "thou shalt not use pronouns without antecedent nouns", which are just good rules for living.

I think you might have a communication port conflict or you aren't selecting the correct protocol driver (DF1 Full Duplex or 1747-PIC/AIC+) in RSLinx or in PanelBuilder32 to work with the PV300 Micro that you have.
 
Ken Roach said:
I'm going to propose a new Forum Law for 2007:

"No Allen-Bradley PanelView questions shall be answered unless accompanied by the complete part number of the PanelView terminal."

This Forum Law shall not supplant nor modify the Commandments, including "thou shalt include precise error message text", and "thou shalt not use pronouns without antecedent nouns", which are just good rules for living.
Bravo.

Additionally, I think NO QUESTION WHATSOEVER should be asked without listing the complete catalog number (including revison level, series, etc.) of the equipment in question.

This is regardless of manufacturer. A-B PanelViews should not be singled out.
 

Similar Topics

Dear all, I have panel view micro300 having catalog number 2711-M3A18L1. I need to download application file in it. So please tell me what cable...
Replies
6
Views
9,763
Hello all, Newbie in Siemens, I want to ask if there will be any issue when I download the instance datablock of a certain Function block? Also...
Replies
6
Views
4,401
i am not experienced user of S7-300 PLC and we are having problem now with one of our PLC's. The CPU is stopping for sometimes, causing the system...
Replies
6
Views
4,989
We have a 2711-K3A5L1. Having trouble downloading a program change. Need help with driver and the proper cable assembly. I assumed that if I could...
Replies
21
Views
10,028
Hey folks, I can communicate over RSLinx to a new PV300 with using PIC/AIC+ driver. I go to download and a WinPFT Exception pops up...
Replies
4
Views
3,224
Back
Top Bottom