Omron C200H to PC communication

P Robson

Member
Join Date
Oct 2002
Location
North East England
Posts
1
This is my 1st post and I realy would appreciate some help.
I am trying to access an Omron C200H CPU 21 for fault finding purposes. I have borrowed a LK201 host link and unsing Syswin software. I have recieved the correct dip switch settings from Omron. However when I plug the host link unit into the CPU it switches to error. Am I doing someting wrong? Is there another progamming interface i can use?
 
Last edited:
However when I plug the host link unit into the CPU it switches to error. Am I doing someting wrong?
If this is a C200H-LK201 Hostlink, then your error comes from plugging it on the rack under power. This creates a "Fatal I/O Bus Error." Mount the module to the rack with the power off.
🔨
 

Similar Topics

I have a sysmac omron plc C200H CPU01,only the power led is ON,using CX-ONE programmer software, and connecting to the plc via Host link LK202-V1...
Replies
2
Views
668
In order to upgrade a control unit, we need to backup program of an omron C200H CPU01 with host link LK202-V1 that has RS422 D9 Connector. Please...
Replies
2
Views
615
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards. The current problem is...
Replies
2
Views
1,021
I am trying to display some scaled analog input values on a C-more Micro terminal, from an older C200H Omron PLC. The addresses appear to simply...
Replies
5
Views
2,121
I have a customer with the Omron C200H that occasionally will start flashing the alarm light and the machine stops. They say they can power down...
Replies
10
Views
2,849
Back
Top Bottom