PLC S7 Disconnect Problem

Brent Tehini

Member
Join Date
Jan 2010
Location
Johannesburg
Posts
2
Hi, some assistance would be greatly appreciated with the S7-300 disconnection problem I am experiencing. The disconnection occurs randomly between the Gateway Server (Server 2003) and PLC. Then automatically reconnect after 30 seconds. This PLC is used to control a High speed sorter. There is a profibus connection to the PLC which receives Bar-coded information from a Datalogic Scanner. The PLC passes this information onto the server to enable correct sortation. The PLC is connected via Ethernet to the Gateway via a simple 8 port switch. During this disconnection we are still able to ping the PLC via the gateway and still receive alive message confirmation.
 
After some long investigation, we found that the TCP offload engine was prematurely disconnecting the port connections. Via registry alterations we were able to disable this "Function" and solve the disconnect problem. Hope this helps anyone battling with the same issue.
 
What's great about this thread is you thought enough of others to return with your solution.

Glad you fixed your problem and many thanks for contributing!
 

Similar Topics

how to generate alarm when PLC & its components like Input Output cards disconnect from Network using Un managed switch 1783 US8T. and PLC is...
Replies
1
Views
1,498
Too often I find that there is a need to lock out all motors, etc on a machine with a single disconnect, yet I don't want to power down the PLC...
Replies
12
Views
7,270
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
31
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
57
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
2
Views
82
Back
Top Bottom