Just curious about something. This card is a 4 point relay output card so it only has 4 outputs. But in the Controller tags when you look at that card it shows 8 bits. See picture
 
Just curious about something. This card is a 4 point relay output card so it only has 4 outputs. But in the Controller tags when you look at that card it shows 8 bits. See picture

That is because it uses the 8-point "Module-Defined Data-Type".

This happens a lot for many modules, as it saves having to have unique data-types for all the modules.

You simply ignore the upper 4 channels.
 
I figure Rockwell had a choice between using four BOOL elements and using a SINT with four unused points, and chose the latter for consistency.

Consider the 1734-IB4D modules I'm using with NO/NC complementary output prox switches. The first four bits give me the status of the four actual input points, and the second four bits give me open-wire/short-circuit status for those input points.

You will find that sort of thing elsewhere in the ControlLogix world; some 16-point input modules have a 32-point data tag, even though they don't use it. It's just easier for the Studio 5000 developers, the firmware developers, and us users to have consistent datatypes for modules that are members of the same family.
 

Similar Topics

Just looking at the manual for 1734-OW4 and it states its "4 type A Normally Open electromechanical relays" but right below it there is a spec for...
Replies
5
Views
2,491
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
2
Views
105
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
195
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
327
Hi all, This is my first time working with a 1734-IE2C analog module. I am tasked with wiring the flow meter into the analog card and the OEM is...
Replies
2
Views
155
Back
Top Bottom