FT View SE device alarms not working

I am following the video https://youtu.be/9SraamBC-Z8.
- My controller is Emulate
- I am using PlantPAX v4.0
- Attached you can see what I configured, with the result that a P_AIn tag goes into alarm (shown in the faceplate) but does not show up in the Alarm Summary

Any suggestions?
  Reply With Quote
Old December 30th, 2022, 03:02 PM   #2
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,279
PlantPAX4.0 does not use Device Tag Based alarms... that's why. There's a tool that comes with PAX4 to create the alarms in a format you can import.
  Reply With Quote
Old December 31st, 2022, 11:59 AM   #3
patjdixon
Member
United States

patjdixon is offline
 
Join Date: Nov 2018
Location: Lago Vista, TX
Posts: 46
Thanks, but tag alarms aren't working either

Now I get it. PlantPax v5 provides device alarms, v4 doesn't.

The problem I have now is getting tag alarms to work. Before I go through the process of using the Alarm Builder, I want to confirm I can manually configure alarms. Attached you can see I tried adding alarm and event tags. None of them are showing up in the Alarm Summary. It is hard to figure out if the problem is in the alarm configuration, the alarm server, or the Alarm Summary configuration
  Reply With Quote
Old December 31st, 2022, 12:15 PM   #4
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,279
Did you save when you added the alarms?



Is the shortcut correct? How is the alarm display configured? Is it pointed at your alarm and events server?


Edit: I'd look at what transformation you'd need to put your alarms in the PLC directly. It's quite nice this way, and it allows you to play with a lot more things by accessing to the @Alarm and @alarmSet tags. Sadly, documentation is close to none about this, although it's something that Rockwell did well to develop.
  Reply With Quote
Old January 1st, 2023, 02:39 PM   #5
patjdixon
Member
United States

patjdixon is offline
 
Join Date: Nov 2018
Location: Lago Vista, TX
Posts: 46
cardosocea, thanks very much for your help!

Q: How is the alarm display configured? Is it pointed at your alarm and events server?
A: I had a typo in the alarm server configuration, now it works

You say I could use @Alarm and @alarmSet tags and there is little documentation of this. How would I use them?
  Reply With Quote
Old January 3rd, 2023, 06:44 AM   #6
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,279
When you create a tag based alarm in the PLC, you can access all of the alarm settings and state with the @Alarm keyword.

If you have several alarms tied to the same variable(or AOI instance), you can then monitor the state of all alarms through the @AlarmSet keyword. The issue is that this functionality isn't described by Rockwell in any detail so it's a bit of a hit and miss. Also, since you don't get access to the internal logic of PlantPAX5, you can't see how they're supposed to be used in the PlantPAX5 topology.

I've asked Rockwell for help on this, but they are true to their fame and told me to Eff Off, but in nicer words. I do have monthly meetings with them about all sites in the company and am planning to drop the bomb in one of these meetings that I don't think it's worth continuing to integrate such a limited platform when we get more bang for our back with even Emerson.

Edit:

In your PLC, create an Analog Value tag. Then right click and add alarm, add the alarms for Hi and Lo (the creation menu has these options). Then in logic (the @Alarm doesn't show in the tag database), create dummy moves to see the values of the different members of the @Alarm UDT for each alarm. Play with the value of the variable to see the difference in data on that @alarm tag.

PlantPAX5 does make use of this functionality... however, they don't make use of the High and Low Alarms and instead configure all as digital alarms (which again is typical Rockwell to make something that isn't usable). My gut feeling without seeing the logic is that they don't have gate functionality in the tag based alarms and have to do it as digital to be able to implement the tag. But I may be wrong on the reason, doesn't matter.

Last edited by cardosocea; January 3rd, 2023 at 06:51 AM.
  Reply With Quote
Old January 24th, 2023, 03:43 PM   #7
patjdixon
Member
United States

patjdixon is offline
 
Join Date: Nov 2018
Location: Lago Vista, TX
Posts: 46
Thanks

cardosocea, thanks!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FT View SE clients dsiplays and popups freezing. bfranklin LIVE PLC Questions And Answers 13 December 16th, 2021 11:31 AM
FT View SE Client couldnot read tag values from the rsLogix 500 Emulator bdauliya LIVE PLC Questions And Answers 2 October 21st, 2020 01:49 PM
FT View SE Recipe Configuration Bullzi LIVE PLC Questions And Answers 7 August 12th, 2016 05:48 PM
FT View SE Editing Without License Mark Cole LIVE PLC Questions And Answers 9 November 22nd, 2014 10:03 AM
Older FactoryTalk View not working with newer FT Services Platform MartyMaucher LIVE PLC Questions And Answers 1 June 5th, 2014 04:43 PM


All times are GMT -4. The time now is 06:41 PM.


.