Hello everyone,
We have an L32 processor on 192.168.1.x subnet and our corporate is now asking us to connect all our machines to their network because they are working on a visualization software for machine performance. All of the other processors that we have are equipped with dual IP except for this one machine which has the older L32 processor which I mentioned above. The corporate network is on 10.74.193.xxx subnet. I tried using the stratix switch VLAN routing but I could not get the corporate to see the PLC. The corporate is using a CISCO 900 switch on their end where the machine will connect to and they established a Vlan 300 on that switch with a specific port for this machine (again, subnet is 10.74.193.xxx). Again, the devices at my disposal are the stratix switches and also I have a MOXA 102 NAT device. Has anyone been able to achieve this and what device did they use? Any technical help will also be much appreciated. regards, Karinrinkashi |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
That Moxa NAT-102 should work very nicely for this purpose.
I can't give you step-by-step directions for setting it up for 1:1 NAT, but can mention that TCP Port 44818 is used by Rockwell Automation for unscheduled communication with ControlLogix / CompactLogix, so you definitely need to allow that port number. |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Nov 2017
Location: Atlanta, GA
Posts: 36
|
![]() Quote:
If anyone else has any suggestions, please do post. |
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
One common misstep with setting up NAT is assigning a gateway address to your L32E, which would be the local IP address of your NAT.
For example, if you NAT has an IP address of 192.168.1.254, you need to assign your PLC's gateway address to 192.168.1.254.
__________________
Open source python communications library for CompactLogix/ControlLogix/Micro800 PLC's: https://github.com/dmroeder/pylogix |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Connecting 2 PLCs on same network. | HoldenC | LIVE PLC Questions And Answers | 5 | May 10th, 2021 06:18 PM |
Plant Network - VLANS VS Subnets? | russg | LIVE PLC Questions And Answers | 10 | January 27th, 2021 10:01 AM |
Connecting profinet - company network | userxyz | LIVE PLC Questions And Answers | 14 | March 14th, 2019 10:51 AM |
Wireless plant network | ASF | LIVE PLC Questions And Answers | 8 | October 14th, 2014 12:56 AM |
s7 200 | gaannesh | LIVE PLC Questions And Answers | 10 | April 21st, 2008 01:33 AM |