anyone KNOW THE MAINT CODE TO RESET THE "REPLACE FAN" HOURS RUN REGISTER IN ACS800 DRIVE. DID IT FEW YEARS BACK BUT CANT REMEMBER.
Why not give ABB Tech Service a call----800.752.0696 Option 1 and Option 1. Knowledgeable friendly people during business hours in Milwaukee WI and NO CHARGE!
Good day, unfortunately I did not come right. I have 20 of these drives. ABB South Africa says I have to send the drives to them or bring their technician onsite which is not practical.Did you get anywhere on this? Having the same problem.
SOLUTION
Okay so I made this account JUST to reply and solve this problem for everyone...
To reset the fan counter do as follows
Go to parameter 16-03
-enter 2303 as passcode
-press enter
-"..." Should appear for a brief moment
Go to parameter 145 (yes 145 now exists, before it only went to 99)
-go to sub-parameter 13 Titled "FAN ON-TIME"
-Press enter
-now you must hold the down arrow until you have brought the hours down to zero. This will take some time as it only decreases in increments of 10, my counter is at 50 000+
-once back to zero press enter. Problem solved, drive should run immediately if being called on to start
Go to parameter 16-03 again
-Press enter
-enter 358 as passcode
-press enter
Now you are done. ACT button out and let fly!
Hope this helps everyone reading this in the future