red lion da30d / Bulletin 1420 power monitor 500

jimcav

Member
Join Date
Dec 2004
Location
new jersey
Posts
229
good morning all


I have several red lion da30d using crimson 3.0 on the controls network in the plant. I am thinking about getting the AB power monitor 500 or 1000. both units talk ethernet/ip. can I have the AB power talk directly to the da30d.


Thank
 
I don't know about the 500/1000 series but I have connected an OPC server to the 3000 series, originally, these were connected via RSPower, the protocol and addresses are the same as the SLC500 so if the RED Lion will communicate with the SLC then providing the 500/1000 series use the same protocol as the 3000 then there should be no problem.
Here is the link to the 3000 manual, it shows the file numbers there:
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1404-um001_-en-p.pdf
 
That is a very good question and I'm glad you asked it before buying the hardware !

I do not have direct experience with the PowerMonitor 500 or 1000, but I've used the 1402, 3000 and 5000 so I know it's worthwhile to verify any assumptions you make about the communications features.

The Red Lion DataStations cannot act as an I/O "Scanner" on EtherNet/IP, nor can they directly read Assembly Objects or other CIP Objects. They can read and write ControlLogix native tags, as well as PLC/SLC/MicroLogix data tables. And of course they have good Modbus RTU and Modbus TCP drivers built into Crimson.

My reading of the PowerMonitor 500 user manual is that its normal communications with a ControlLogix are over I/O connections to the Assembly Object. It does all of its configuration comms with Modbus/TCP. So that's a bit of a weird mix of protocols that likely comes from the PM500's origin based on a third-party product.

It is likely that you could use a PowerMonitor 500 with the DataStation, using Modbus/TCP only. The summary of data tables starting on page 57 of that user manual makes sense to me.

The PowerMonitor 1000 has a lot more variety of interfaces and protocols. The serial port supports DF1 and Modbus and even an ASCII console.

The Ethernet port is relatively low powered (10 Mb/s, half-duplex) and supports Modbus/TCP, native EtherNet/IP objects including an I/O Assembly and various data Assemblies, and PCCC data table emulation.

The most useful for your purposes is the "PCCC data table emulation". This allows the PowerMonitor 1000 to emulate a classic Allen-Bradley PLC data table. The addressing table in Appendix A of the user manual is very useful.

For example, the Volts/Amps/Frequency monitoring data is presented as Data Table address F21:0-19.

In Crimson or any other HMI software, you would configure the PowerMonitor 1000 target like a MicroLogix 1100/1400, rather than like a legacy PLC-5E or SLC-5/05.
 

Similar Topics

Hi folks, I'm trying to parse a binary string on a Red Lion DA30D using a Raw UDP/IP input port. I've done this before with ASCII strings so I do...
Replies
38
Views
969
I need a CQM1H-CPU51 to talk to my Red lion Da30D i just need to read the status of some I/O and maybe read some data registers but I cannot...
Replies
7
Views
1,157
We have two Red Lion DA30D units that keep dropping off the network. They are configured as 10.4.7.1 and 10.4.7.2 they work for so long then just...
Replies
24
Views
12,437
While they came up quickly with a fix for the alarm date issue quickly I will have to drive around for a week or so, burning up a lot of fuel...
Replies
4
Views
245
From the Red Lion website, after some customer enquiries in the last week or so... Rev. March 25, 2024 [18:30] Just thought it might help a...
Replies
9
Views
275
Back
Top Bottom