anybus rs232 to ethernet

Cajmccormick

Member
Join Date
Aug 2018
Location
Ontario
Posts
12
has anyone used an anybus module or some sort of serial to ethernet converter with a control logix plc? If so how did you translate/parce specific serial data into the plc via ethernet.

thanks
 
I've not used the Anybus device however I do know of a way to easily do what you are trying to do and you won't need to convert/translate any data.
Spectrum Controls is about to release their new Universal Gateway which will bridge a ControlLogix PLC to a serial device as long as the serial device is either DF1 or Modbus RTU (or ASCII).
You can reach out to their application support for more detailed information (it really is very simple to use)

https://www.spectrumcontrols.com/products/webport-solutions/universal-gateway/
 
Serial to EtherNet

I worked on a Contrologix to CanBus Anybus about a year ago. I did not write the code, but I did have to debug some of it.

If I still have the code I will browse through to see if it may help you.
 
What exact model of HMS device are you using ?

Is the data bi-directional, or uni-directional ?

How is the data encoded ? Ordinary ASCII with carriage returns and line feeds ? Fixed-length strings ? Data delimited by time ?
 
What exact model of HMS device are you using ?

Is the data bi-directional, or uni-directional ?

How is the data encoded ? Ordinary ASCII with carriage returns and line feeds ? Fixed-length strings ? Data delimited by time ?

It is an HMS-EN2SE-R;

Data will be bi-directional;

Ordinary ASCII Data;
 
The anybus is quite good if you need to roll your own protocol.

I had to use it to talk to a bunch of rs485 multidropped digital position indicators and it was reasonable straightforward.

Configure data exchange dialogs and schedules and it will automatically extract/insert data from the stream and create CRCs and checksums if required. The data is exchanged to the plc as a memory image.

If it is something well known you can probably get something off the shelf to do it for you.
 
I have used Anybus for RS232 to Ethernet IP before. It took a little to set it up, but Anybus tech support is quite good.
After they know you are trying to do it your self and are struggling, they will help.
I had a real nice lady in TS that sent configurations back and forth with me to get it working correctly.
 
Digi One IAP - it can be used as a virtual COM port to the computer, or do serial protocol to Ethernet protocol conversion (Ex. DF1 to Ethernet/IP). It also has a passthrough feature, where, if you have a PLC and HMI connected via Serial Cable, you can attach both to the Digi One IAP, and have access to both over Ethernet, while maintaining the direct serial connection at the same time.

https://www.digi.com/products/netwo...rial-hardened-serial-servers/digioneiapfamily
 
RTA Automation makes the most user friendly serial-to-ethernet gateway I've used. We used it to collect data from serial barcode readers and rundown data from Atlas Copco Powerfocus controllers.
 
I have not used the EN2SE-R itself. My understanding is that it is a new generation of the HMS Communicator, equipped with a Rockwell DLR capable dual-port Ethernet interface, and with a configuration applet embedded into an Add-On Profile (AOP) so that it can be configured entirely within Studio 5000.

But I have used the original HMS Communicator, with the HMS Configurator utility.

For ordinary ASCII with terminating characters (like CR and LF), these are very easy to use. In the array of data that arrives as the I/O packet, there's an incrementing counter that increases by 1 to let you know that a new string is in the Input data array . Another element of the array is the Length of the string, and the rest of the array is the bytes in the string.

All you have to do is write code that essentially says "If InputCounter > InputCounterOld, copy Input data to String and set InputCounterOld := InputCounter"


The output is similarly straightforward; you copy the Length and Data bytes into the Output array, then increment the Output Data counter by 1, which causes the module to send that data out of its serial port.

In my opinion, the Communicator's ease-of-use is second only to that of the RTA Gateways; those send data directly to ControlLogix Tags that you configure by name in a web browser interface. The upcoming Spectrum Gateway works in a similar way.

I don't think it's speaking out of school too much here to say that HMS discovered a serious bug in the EN2SE and its related modules last year that led to a short stop-sales order and led me to use a competitive product. That actually makes me more confident in the current stability of the module and the competence of the HMS worldwide distribution and support network.
 
has anyone used an anybus module or some sort of serial to ethernet converter with a control logix plc? If so how did you translate/parce specific serial data into the plc via ethernet.

thanks

It's more cost effective to make your own these days.
A Pi type board with Linux installed.
I just bought one with PCI-e and a 8 port serial card, can build an RS-232 to Modbus TCP network for around $300 with 8 serial ports.
 

Similar Topics

Hello all and happy Friday, I'm curious if anyone here has experience sending data over an Anybus Bolt II (HMS AWB6001-A) using a Compact Logix...
Replies
4
Views
742
We have a keg check weigher that that lost a fight to a forklift. The scale was previously a Systec IT3000, which was the only PROFIBUS slave...
Replies
5
Views
646
Complete novice trying to integrate an industrial fluid filling process into MES using an anybus communicator Hardware: Anybus Communicator...
Replies
3
Views
1,566
Hi, does anyone here sell the cable for the classic Anybus "PC connector"? I have a customer who has an old machine and he would like to retrieve...
Replies
5
Views
1,811
We have been using ProfiBus Gateways to connect to a piece of equipment. The equipment interface is through a PB/PB adapter that we connect...
Replies
2
Views
1,805
Back