RSLogix 5 Trend Problem, can't see trend on another PC

harryting

Lifetime Supporting Member
Join Date
May 2002
Location
Puget Sound
Posts
2,594
Help from you Rockwell gurus please.

Got this nice trend created in RSLogix 5. Works fine in one PC but when I went to another PC the trend don't work. More precisly, none of the pens configured shows up. I updated both PC to the newest CPR 6. Still no luck.

On the one PC where the trend don't work; the trend does appear in the Trend Listing with the right name. Also, I noticed, on one of the PC, under the PEN tab, there is a button "Load Pen List" which is not available on the other PC. So it make me think there is trend version issue. But both RSLogix installation is the same version?!

Can't find anything on Rockwell's KB
 
Update:

I *fixed" it. I checked into TrendX and found a difference in version #; 3.40 vs 3.41. So I dug out a RSView32 Extension CD and installed the newest version of TrendX on all. The bad thing is that it wiped out TrendX configuration I did (To Rockwell: YOU GOT TO BE KIDDING). The good thing is TrendX works now across different PC.
 

Similar Topics

I have a SLC 5/04 and I am trying to figure out how I can trend the temperature of some heaters and a binary machine running signal into an excel...
Replies
3
Views
1,424
Hello PLCS.net! Here again to ask about how to do some weird quirky thing with RSLogix 5000. I see my team trending a lot of tags, but it becomes...
Replies
0
Views
1,530
I have been primarily working on Controllogix projects as of late, but today I opened up one of our PLC5 programs and when I went to set up a...
Replies
10
Views
3,696
hi, how long will the trend accumulate data? Forever, or will it start scrolling over itself eventually? I set it to refresh every...
Replies
0
Views
1,859
Hello :scratch:, I work in a Gas Transmission plant running all ControlLogix 5000's with Panel View 1000's w/ Factory Talk View Studio ME...
Replies
14
Views
28,639
Back
Top Bottom