Difference between Sinamics S 120 & Simotion D - Siemens Drive
Jun 2017
Coimbatore- Tamil Nadu
Hi all,
I'm newly joined in this website. Hope all are fine.
I'm very new to PLC and Drive system and interested to learn about this.
I want to know what is the main difference between Sinamics S120 & Simotion D - Siemens drive.
Thanks in advance.
Regards
Sabari
Simotion D is a drive-based motion controller, and Sinamics S120 is a servo drive system.
The modular style of Sinamics S120 is typically a Control Unit (CU), Power module (PM), and Motor Module(s) (MM). The CU connects to a higher up PLC or Motion Controller, PM is the AC Power Supply for the MM(s). The MM(s) is/are connected to the motor(s).
From the above example, if you replace the CU with a Simotion D controller, then you have a standalone, drive-based motion controller, on the Sinamics S120 platform.
Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
1,410
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
28
4,023
Good Morning , I have 2 Frequency Drive panels to build and commission . It is for 2 pump systems . Just wondering , what is the...
1,968
Hi Experts, Good day! What are the differences between PCS7 SIMATIC Batch and PM Control? Do you have any manual like "Getting Started "...
809
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
2,816