AB Micro1400 PID AntiWind Up
dave k
Jan 2011
ny
26
Team,
I am using a Allen Bradley Micrologix 1400 and I think I am experiencing Anti Wind Up in my PID Instruction.
Any suggestions on how to prevent this?
Any suggestions on Best practices using PID Instruction?
My PID Instruction is on an unconditional rung and I am switching between manual and automatic modes, not sure if this is a problem?
any suggestions would be greatly appreciated.
thanks
o_O
What are the conditions for the switching?
What is it controlling? Speed, pressure, temperature? What is the sensor and actuator/s?
What are you observing?
I am controlling a dc motor speed so when the motor is disabled I put pid in manual and when the motor is enabled I put pid in auto mode.
the sensor is an encoder for position and speed
it appears when I am going from manual to auto the output jumps to full output and stays there for a while before it drops.
When you go from manual to auto, can you set the integral to whatever the manual value was?
I am pretty sure what is wrong.
I am not surprised.
What is your set point?
How do you change your set point?
There was a similar thread a week or two ago.
Does the amplifier have velocity loop or is it a simple voltage to current amplifier?
Need more info. There should be no windup if you're in manual and writing to the output directly. Bumpless transfer is inherent from manual to auto if done correctly.
I have a micro1400 processor running two routines (transfer compression/compression molding press). Recipe parameters are stored from job to job...
28
Hi everyone, I have a Micrologix 1400 using an HSL instruction (High Speed Counter Load). This instruction is used in junction with an encoder...
813
Hey All, making progress with my Applied Motion Drive. SV200. however to properly convert decimal to hex, byte swap and message the conversion...
1,860
The micro has ethernet embedded, the panelview has ethernet embedded. It is replacing like components that was using DH485 with an AIC+ between...
2,730
Just getting started with programming and playing around a bit with some equipment we have here at work. Here is what I have: Banner Ultrasonic...
2,285