rslogix5000 1 sec pulse
muds
Apr 2014
karachi
71
HI ,,
I Want to create 1 sec pulse in rslogix 5000.
can anyone tell how to create this. so that i can calculate machine runtime.
thanks,
HI ,,
thanks,
How much do you want to count up to ?
Why not use a RTO (Retentive Timer-On) set for 1 hour, and a counter to count hours.
2,147,483,647 hours is 89,478,485 days, or more than 245,146 years !! I think much more than enough for the application....
I pity that poor maintenance technician on 245,147 years
And probably won't have the right version either.
I use the system clock for this, built an AOI to handle it but essentially I'm using a GSV to get the WallClockTime parts. I then use a one shot rise/fall on bit.0 of the time part I am interested in to create a second/minute/hour...etc pulse.
That pulse is then used with a counter in various parts of the program where needed.
Note, my AOI is in ST and has output bits for sec/min/hour pulses.
Not an original design
It's fairly accurate.
It's only as accurate as it can be, bearing in mind you haven't accounted for the timer accumulator being greater than 1000 which it can be, depending on how frequently it is scanned.
The error will always be positive, so your "Tick" will always be longer than 1 second.
HI ,,
thanks,
You don't need a 1 second pulse bit if you create a program within a 1000 ms periodic task. You can then simply operate your math statements unconditionally and they will be processed once per second.
You should know that you'll eventually run into rounding errors if totalizing with floating point math, unless you take measures to prevent this from happening.
Paully I like your approach, I do not want to reinvent the wheel, can you post it ?
Here is the ST, the AOI parameter input/output definitions should be pretty obvious.
Code:
// Get PLC Time
GSV(WallClockTime,,localdatetime,DateTime[0]);
// Parse out PLC time to friendly format
year := DateTime[0];
month := DateTime[1];
day := DateTime[2];
hour := DateTime[3];
minute := DateTime[4];
second := DateTime[5];
microsecond := DateTime[6];
// 1 Second pulse generation
// Triggered by the rise/fall of bit 0
SecondOSR.InputBit := second.0;
OSRI(SecondOSR);
SecondOSF.InputBit := second.0;
OSFI(SecondOSF);
secPulse := (SecondOSR.OutputBit OR SecondOSF.OutputBit);
// 1 Minute pulse generation
MinuteOSR.InputBit := minute.0;
OSRI(MinuteOSR);
MinuteOSF.InputBit := minute.0;
OSFI(MinuteOSF);
minPulse := (MinuteOSR.OutputBit OR MinuteOSF.OutputBit);
Let me count the ways
The most commonly found in code (also the most inaccurate, but good enough for Motor Run Times
AUX OneSecTmr.DN OneSecTmr
+------TON --+
---| |------------|/|-----------| PRE: 1000 |
Use the OneSecTmr.DN bit as your pulse.
The inaccuracy in this code is on the order of 2% ± short. You lose one full scan, plus the overrun of the scan time when the TON was last executed.
Since the "Run Time" is mostly for guestimating ("That's a lot of time; we should get ready to service it") or comparison ("Motor A has more run time than Motor B"), accuracy isn't an issue.
The code that John Morris posted is a more, but not perfectly accurate. It eliminates the missed scan (for not-true TON to reset the .DN bit), but still loses scan elapsed time (as daba pointed out)
Presumably you are counting seconds to display hours. If you use a TON to actually time hours, you lose lots of fractional hours each time the motor turns off. A Retentive timer prevents that loss, and putting the reset before the timer means that the DN bit will be on for one scan.
OneHrPulse.DN OneHrPulse
----------| |-------------[ RES ]
AUX OneHrPulse
+----------RTO--+
--------| |------------| PRE: 3600000 |
The amount of inaccuracy in this timer is on the order of .001%. More than good enough for Run Time, and if you want to include fractional hours, just add your integer hour count + ACC/PRE.
The most accurate 1 sec pulse counter is to
AUX RUNNING_TMR
+-------------RTO--+
--------| |------------| PRE: 2147483647 |
+-----------GRT---+ +------------SUB---+ OneSecPulse
----| RUNNING_TMR.ACC |--------| RUNNING_TMR.ACC |---------( )-
| 1000 | | 1000 |
+-----------------+ | RUNNING_TMR.ACC |
The timer never DONEs out, and is never reset. But it also never accumulates more than 1 second of total elapsed time. It never loses the scan overruns.
Overkill for a Running Time counter, but is as accurate or more as using a Timed Task.
I used this method (retentive timer) with a customer that wanted run time for different pumps to estimate when to perform maintenance on them.
You are correct kind sir, but the application didn't call for T*Ts on timing. It just needed to count out ten minute cycle times, +/- 2 or three seconds was ok.
I wouldn't have used it for high speed bottling/canning.
I figured it would have suited the OP's request.
I need to take seconds and convert to mm:ss. Say i have a cycle that the operator of a machine wants to run for 125 seconds. He will enter 125...
4,236
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
409
Hello everyone, I have an RSLogix5000 project which is running live in the factory but I need to make some changes to the logic. I want to test...
1,113
Good Morning Everyone, I'm looking to use the GSV instruction to get I/O fault codes for my project so I know if there's a comms issue in my E/IP...
853
The machine is running production. When trying to go online with the laptop the whole machine looses communication and faults out. Drives, HMI...
1,920