3P + N + E with E and N the same

The ground conductor between the service and your equipment will be carrying current. This is a no-no.

Totally agree with Okie.

The ground wire is electrically different from the Neutral. The ground is not supposed to carry current under normal conditions. The neutral is The return path for your single phase loads.

Make them provide a 5-wire service to your machine.
 