Dick,
NEC Article 250.20 requires all AC premise wiring systems to be grounded, EXCEPT as denoted in 250.21. Then 250.21.A.1-4 list specific cases where they CAN be ungrounded, but then 250.21.B says IF you do that, you must add a "ground detection system" at the service point and use specific signage (which nobody does). The Ground Detection System will cost you more than just corner-grounding the transformer.

But as you know, in VFD world a corner grounded delta system might as well be ungrounded as far as the VFD is concerned, so be careful about recommending that. I just use the argument to get people to stop using UNGROUNDED delta and switch to (or create) a wye system if they are going to have any power electronics.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT Wye delta transformer 30 degree phase shift - why leitmotif LIVE PLC Questions And Answers 12 October 24th, 2018 01:41 PM
DELTA PLC and VFD DELTA CONNECTION ISSUES. macub3x010101 LIVE PLC Questions And Answers 0 August 6th, 2017 10:57 AM
Issues with delta HMI rejoe.koshy LIVE PLC Questions And Answers 9 February 11th, 2017 12:28 AM
SLC 5/05 to Delta Motion 75E mikeyboy LIVE PLC Questions And Answers 6 January 5th, 2009 03:17 PM
Running 300 volt rated Devicenet cables with 600 Volt power wiring metal_pro LIVE PLC Questions And Answers 16 October 27th, 2006 01:30 PM


All times are GMT -5. The time now is 04:39 AM.


.