Old November 20th, 2020, 02:25 PM   #1
Don Diego
Member
Ghana

Don Diego is offline
 
Join Date: Apr 2017
Location: Tema
Posts: 11
Alarm

I want an alarm / indicator when a contact fail to close in stipulated time , I am finding it difficult writing this rung. Need help


Wisdom Samlafo
Facebook /Wise Samlafo
Ghana
  Reply With Quote
Old November 20th, 2020, 02:44 PM   #2
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,478
Command_Close + Not_Closed Start_Timer


Timer_Timed_Out = Alarm.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old November 20th, 2020, 02:55 PM   #3
Don Diego
Member
Ghana

Don Diego is offline
 
Join Date: Apr 2017
Location: Tema
Posts: 11
Rdrast,
Can you write the rung/instruction in ladder logic ? It's beyond my head
  Reply With Quote
Old November 20th, 2020, 04:50 PM   #4
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
This is probably more than the OP asks for; remove the blue code sections for the bare minimum.


Behavior
  • An Event occurs at time T
  • If The_Coil closes before time (T+10000ms), then there will be no alarm
  • If The_Coil does not close before time (T+10000ms), then there will be an alarm.
    • The alarm is triggered by the PLC output Alarm_Out changing from 0 to 1
    • If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, even if The_Coil closes.


External devices
  • Event
    • Physical contact that initiates the process
  • The_Coil
    • Physical relay that must close within 10000ms of contact Event
  • Coil_feedback
    • Physical contact feedback on The_Coil, that closes when The_Coil closes
  • Alarm_Reset_Button
    • Momentary button to reset alarm

PLC Inputs
  • Event_In
    • NO: input that detects (becomes 1 on) closure of contact Event
  • Alarm_Reset_In
    • NO: input that detects (becomes 1 on) closure of contact Alarm_Reset_Button
  • Contact_in
    • NO: input from Coil_feedback that detects (becomes 1 on) closure of The_Coil
    • N.B. this is related to, but separate from, Contact_Out

PLC Outputs
  • Contact_Out
    • Output to drive The_Coil, which The_Coil should close] within 10000ms after Event_In becomes 1
    • This output, and the blue branch below, are not necessary if external device Event is physically wired to close The_Coil, external to the PLC
  • Alarm_Out
    • Output to alarm if input Contact_In does not become 1 (indicating that The_Coil has not closed) within 10000ms after Event_In becomes 1




Sections in blue are optional and extra bells and whistles:


Code:
    Event_In        Contact_in     _____________
-----] [------+--------]/[--------[TON        DN]-----+-----
              |                   [Name  the_ton]     |
              |                   [PRE     10000]     |
              |                   [Acc         0]     |
              |                    -------------      |
              |    Contact_Out                        |
              +--------( )----------------------------+


       the_ton.DN       Alarm_Reset_In    Alarm_Out
----+-----] [-------+---------]/[------------( )--------
    |               |
    |   Alarm_Out   |
    +-----] [-------+
Minimal case:

N.B. this assumes Event is wired directly to The_Coil


N.B. in this case, when Event_In is 1 and an alarm has been triggered, that alarm will stop if the The_Coil closes.



Code:
    Event_In        Contact_in     _____________
-----] [---------------]/[--------[TON        DN]-----------
                                  [Name  the_ton]
                                  [PRE     10000]
                                  [Acc         0]
                                   -------------


       the_ton.DN           Alarm_Out
----------] [------------------( )--------
  Reply With Quote
Old November 23rd, 2020, 06:38 AM   #5
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
I thought some more about this, and my previous post #4 may have the reset logic in the wrong place, as it allows the operator to suppress the alarm by laying a wrench on the reset button.


Corrected logic is below.




Behavior
  • ..
  • If The_Coil does not close before time (T+10000ms), then there will be an alarm.
    • The alarm is triggered by the PLC output Alarm_Out changing from 0 to 1
    • If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, after either The_Coil closes or Event_In becomes 0.


External devices
  • ..
  • Alarm_Reset_Button
    • Momentary button to reset alarm after either Event becomes 0 or The_Coil closes (Contact_In becomes 1).




Code:
    Event_In        Contact_In     _____________
-----] [------+--------]/[--------[TON        DN]-----+-----
              |                   [Name  the_ton]     |
              |                   [PRE     10000]     |
              |                   [Acc         0]     |
              |                    -------------      |
              |    Contact_Out                        |
              +--------( )----------------------------+


       the_ton.DN                            Alarm_Out
----+-----] [------------------------+-----( )--------
    |                                |
    |   Alarm_Out    Alarm_Reset_In  |
    +-----] [------------]/[---------+

Last edited by drbitboy; November 23rd, 2020 at 07:14 AM.
  Reply With Quote
Old November 24th, 2020, 03:16 PM   #6
Robb B
Member
Canada

Robb B is offline
 
Join Date: Feb 2011
Location: canuckistan
Posts: 91
Quote:
Originally Posted by drbitboy View Post
I thought some more about this, and my previous post #4 may have the reset logic in the wrong place, as it allows the operator to suppress the alarm by laying a wrench on the reset button.


Corrected logic is below.




Behavior
  • ..
  • If The_Coil does not close before time (T+10000ms), then there will be an alarm.
    • The alarm is triggered by the PLC output Alarm_Out changing from 0 to 1
    • If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, after either The_Coil closes or Event_In becomes 0.


External devices
  • ..
  • Alarm_Reset_Button
    • Momentary button to reset alarm after either Event becomes 0 or The_Coil closes (Contact_In becomes 1).




Code:
    Event_In        Contact_In     _____________
-----] [------+--------]/[--------[TON        DN]-----+-----
              |                   [Name  the_ton]     |
              |                   [PRE     10000]     |
              |                   [Acc         0]     |
              |                    -------------      |
              |    Contact_Out                        |
              +--------( )----------------------------+


       the_ton.DN                            Alarm_Out
----+-----] [------------------------+-----( )--------
    |                                |
    |   Alarm_Out    Alarm_Reset_In  |
    +-----] [------------]/[---------+
Both versions work, so nothing "wrong", although the first version would prevent the alarm if the reset is held, while the second version will allow the alarm even if the reset is held. (Held could be a short, broken button contacts, etc). All a matter of preference or requirement.
  Reply With Quote
Old November 24th, 2020, 03:20 PM   #7
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by Robb B View Post
Both versions work, so nothing "wrong", although the first version would prevent the alarm if the reset is held, while the second version will allow the alarm even if the reset is held. (Held could be a short, broken button contacts, etc). All a matter of preference or requirement.



Good point; it will depend on the application.


Thanks.
  Reply With Quote
Old November 24th, 2020, 03:24 PM   #8
I_Automation
Member
United States

I_Automation is online now
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 362
But on your Alarm Out I would add a branch and put a 32 second timer, then if that timer gets DN activate the Operator Training Collar Transmitter (Pet Supplies Plus sells them)
  Reply With Quote
Old November 28th, 2020, 10:09 AM   #9
Don Diego
Member
Ghana

Don Diego is offline
 
Join Date: Apr 2017
Location: Tema
Posts: 11
Plaudits

Quote:
Originally Posted by drbitboy View Post
This is probably more than the OP asks for; remove the blue code sections for the bare minimum.


Behavior
  • An Event occurs at time T
  • If The_Coil closes before time (T+10000ms), then there will be no alarm
  • If The_Coil does not close before time (T+10000ms), then there will be an alarm.
    • The alarm is triggered by the PLC output Alarm_Out changing from 0 to 1
    • If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, even if The_Coil closes.


External devices
  • Event
    • Physical contact that initiates the process
  • The_Coil
    • Physical relay that must close within 10000ms of contact Event
  • Coil_feedback
    • Physical contact feedback on The_Coil, that closes when The_Coil closes
  • Alarm_Reset_Button
    • Momentary button to reset alarm

PLC Inputs
  • Event_In
    • NO: input that detects (becomes 1 on) closure of contact Event
  • Alarm_Reset_In
    • NO: input that detects (becomes 1 on) closure of contact Alarm_Reset_Button
  • Contact_in
    • NO: input from Coil_feedback that detects (becomes 1 on) closure of The_Coil
    • N.B. this is related to, but separate from, Contact_Out

PLC Outputs
  • Contact_Out
    • Output to drive The_Coil, which The_Coil should close] within 10000ms after Event_In becomes 1
    • This output, and the blue branch below, are not necessary if external device Event is physically wired to close The_Coil, external to the PLC
  • Alarm_Out
    • Output to alarm if input Contact_In does not become 1 (indicating that The_Coil has not closed) within 10000ms after Event_In becomes 1




Sections in blue are optional and extra bells and whistles:


Code:
    Event_In        Contact_in     _____________
-----] [------+--------]/[--------[TON        DN]-----+-----
              |                   [Name  the_ton]     |
              |                   [PRE     10000]     |
              |                   [Acc         0]     |
              |                    -------------      |
              |    Contact_Out                        |
              +--------( )----------------------------+


       the_ton.DN       Alarm_Reset_In    Alarm_Out
----+-----] [-------+---------]/[------------( )--------
    |               |
    |   Alarm_Out   |
    +-----] [-------+
Minimal case:

N.B. this assumes Event is wired directly to The_Coil


N.B. in this case, when Event_In is 1 and an alarm has been triggered, that alarm will stop if the The_Coil closes.



Code:
    Event_In        Contact_in     _____________
-----] [---------------]/[--------[TON        DN]-----------
                                  [Name  the_ton]
                                  [PRE     10000]
                                  [Acc         0]
                                   -------------


       the_ton.DN           Alarm_Out
----------] [------------------( )--------
Drbitboy, I think the second Program is much user friendly. It work perfectly on the simulator but, but a reset button between ton. DN and Alarm out will make it even better
  Reply With Quote
Old November 28th, 2020, 10:37 AM   #10
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by Don Diego View Post
Drbitboy, I think the second Program is much user friendly. It work perfectly on the simulator but, but a reset button between ton. DN and Alarm out will make it even better

A momentary button, between [the_ton.DN] and [Alarm_Out], that needs to be pressed and held is not a reset button; it is a [temporary silence/disable alarm]. That's why I improved the code from post #4 to post #5. This may be acceptable, or even necessary if a audible alarm needs to be temporarily silenced.



And a push (or toggle or maintain) button, that stays in once pressed, is also not a reset button; it is an [alarm disable] i.e. it disables the current and all future alarms. This is probably not a good idea; if an audible alarm needs to be silenced then there should be a separate rung, with temporary* logic, for the audible alarm but the HMI alarm should remain.



The way the second set of rungs are written, the alarm is only reset when either
  • the delayed The_Coil finally closes and [Contact_In] becomes 1,
  • OR
  • the trigger event ends and [Event_In] becomes 0.
* "temporary" means it stops the audible alarm for the current alarm, but the audible alarm would be re-enabled for the next such event.
  Reply With Quote
Old November 28th, 2020, 10:45 AM   #11
Don Diego
Member
Ghana

Don Diego is offline
 
Join Date: Apr 2017
Location: Tema
Posts: 11
Quote:
Originally Posted by drbitboy View Post
A momentary button, between [the_ton.DN] and [Alarm_Out], that needs to be pressed and held is not a reset button; it is a [temporary silence/disable alarm]. That's why I improved the code from post #4 to post #5. This may be acceptable, or even necessary if a audible alarm needs to be temporarily silenced.



And a push (or toggle or maintain) button, that stays in once pressed, is also not a reset button; it is an [alarm disable] i.e. it disables the current and all future alarms. This is probably not a good idea; if an audible alarm needs to be silenced then there should be a separate rung, with temporary* logic, for the audible alarm but the HMI alarm should remain.



The way the second set of rungs are written, the alarm is only reset when either
  • the delayed The_Coil finally closes and [Contact_In] becomes 1,
  • OR
  • the trigger event ends and [Event_In] becomes 0.
* "temporary" means it stops the audible alarm for the current alarm, but the audible alarm would be re-enabled for the next such event.
Drbitboy, the problem with the post #5 is the alarm the alarm is still energized with the Alarm _Reset _In open. As long as the _TON _DN is set , the alarm will still be audible even if Akarm_Reset_In is open.
Have you done the simulation, I tried and that's a problem

Last edited by Don Diego; November 28th, 2020 at 10:53 AM.
  Reply With Quote
Old November 28th, 2020, 12:43 PM   #12
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by Don Diego View Post
Drbitboy, the problem with the post #5 is the alarm the alarm is still energized with the Alarm _Reset _In open. As long as the _TON _DN is set , the alarm will still be audible even if Akarm_Reset_In is open.
Have you done the simulation, I tried and that's a problem



That is intentional: there is a difference between alarm reset and alarm disable. If it can be disabled, what is the point of having an alarm?
  Reply With Quote
Old November 28th, 2020, 01:57 PM   #13
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by drbitboy View Post
That is intentional: there is a difference between alarm reset and alarm disable. If it can be disabled, what is the point of having an alarm?



An alternative would be to call it an Alarm Acknowledge, so the operators must acknowledge that there was an alarm condition. It depends on the severity of the condition, i.e. is it important to know that it happened?
  Reply With Quote
Old November 28th, 2020, 03:47 PM   #14
Don Diego
Member
Ghana

Don Diego is offline
 
Join Date: Apr 2017
Location: Tema
Posts: 11
Quote:
Originally Posted by drbitboy View Post
An alternative would be to call it an Alarm Acknowledge, so the operators must acknowledge that there was an alarm condition. It depends on the severity of the condition, i.e. is it important to know that it happened?
....I concur

Different ways of going about acknowledging the alarm , it depends on the application.

Sorry for the late feedback after the initial post; I have been busy all week. I work 12 hours daily from 6am - 6pm at an oil mill as an industrial Electrician, very little free time at my disposal
  Reply With Quote
Old November 28th, 2020, 04:21 PM   #15
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by Don Diego View Post
....I concur

Different ways of going about acknowledging the alarm , it depends on the application.

Sorry for the late feedback after the initial post; I have been busy all week. I work 12 hours daily from 6am - 6pm at an oil mill as an industrial Electrician, very little free time at my disposal

no need to apologize, one of the benefits of a forum is that the conversation is asynchronous, so people can participate as much or as little as they can.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How to make FT Machine Alarm banner automatically disappear suboliu LIVE PLC Questions And Answers 3 June 27th, 2016 02:04 PM
Wonderware alarm acknowledgement question defcon.klaxon LIVE PLC Questions And Answers 7 August 4th, 2015 12:59 PM
Alarm Prevention on Powerup Ken Roach LIVE PLC Questions And Answers 5 June 8th, 2013 08:27 PM
Alarm Handing cjd1965 LIVE PLC Questions And Answers 17 March 11th, 2012 06:23 AM
Maintenance alarm (again) tlvaun LIVE PLC Questions And Answers 2 May 4th, 2003 07:11 AM


All times are GMT -5. The time now is 04:00 PM.


.