Micrologix 1200 to PLX51-df1-eni router

Guys, need help.

How am I going to use this MSG instruction in RS Logix 500 to communicate in PLX51-df1-eni router.

I already configured the df1 router and its already present in RS-linx.
Attached Images
File Type: png Capture.PNG (95.2 KB, 7 views)
File Type: png Capture1.PNG (45.5 KB, 5 views)
File Type: png Capture2.PNG (44.4 KB, 5 views)
File Type: png Capture3.PNG (48.2 KB, 4 views)

Last edited by akosimalakas; November 21st, 2020 at 12:45 AM. Reason: additional information
  Reply With Quote
Old November 21st, 2020, 01:10 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,677
Welcome to the PLCTalk forum community !

What is your application; are you trying to read or write data from another SLC/MicroLogix family controller on Ethernet, or a ControlLogix/CompactLogix family controller ?

Are you asking for help on configuring and triggering an MSG instruction in ladder logic, or on configuring the DF1 Station address -> IP Address routing in the Prosoft device ?
  Reply With Quote
Old November 21st, 2020, 01:17 AM   #3
akosimalakas
Member
Philippines

akosimalakas is offline
 
Join Date: Aug 2020
Location: Manila
Posts: 5
thank you for your reply sir, I already configured the prosoft device. the problem is I cannot communicate the ML1200 to prosoft df-1 router because it doesn't appear in rs-linx. so maybe I need the MSG instruction in order to communicate in prosoft device.

I need to read data in ML1200 using PLX51-DF1-ENI to send it in scada.

Last edited by akosimalakas; November 21st, 2020 at 01:22 AM.
  Reply With Quote
Old November 21st, 2020, 01:54 AM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,677
You definitely do not need MSG instructions to communicate with your MicroLogix from a SCADA system.

The configuration of the PLX router looks correct, and it does appear in RSLinx as an Ethernet device. It's the DF1 port and connected MicroLogix that do not appear.

What sort of cable are you using between the PLX router and the MicroLogix ? Does the COMM LED on the MicroLogix ever flicker when you browse the PLX router in RSLinx, suggesting that packets are moving between the PLX and the MicroLogix ?

You might also try configuring the MicroLogix Channel 0 serial port for Source ID =1 instead of 8. While most DF1 Full Duplex Point-to-Point implementations ignore the Source and Destination station numbers, it might be that the PLX router expects the MicroLogix to have DF1 station address = 1.
__________________
- "Simpler is better, except when complicated looks really cool."
  Reply With Quote
Old November 21st, 2020, 02:44 AM   #5
akosimalakas
Member
Philippines

akosimalakas is offline
 
Join Date: Aug 2020
Location: Manila
Posts: 5
the cable I use to communicate the DF1 router to micrologix 1200 is 1761-CBL-PM02,SER.C
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Micrologix 1200 to PV+ Comm problems m_ryzebol LIVE PLC Questions And Answers 7 March 10th, 2015 11:44 PM
Multiple Micrologix behind a router Russff LIVE PLC Questions And Answers 32 January 27th, 2015 02:42 PM
Comm issue between Micrologix 1200 and PanelView 600 edwinmart LIVE PLC Questions And Answers 5 September 13th, 2008 07:37 PM
PanelView 900 to Micrologix 1200 alfred_fuentes LIVE PLC Questions And Answers 3 January 10th, 2007 10:08 AM
Help with DF1 Protocol command to retrieve N7 integer values from Micrologix 1200 PLC davidgay LIVE PLC Questions And Answers 7 June 28th, 2002 08:59 AM


All times are GMT -5. The time now is 08:41 AM.


.