Old November 21st, 2020, 02:02 PM   #1
RY_Guthrie
Member
United States

RY_Guthrie is offline
 
Join Date: Nov 2011
Location: Las vegas, NV
Posts: 206
rockwwell 525 drive

We are trying to set up a watch dog for a rockwell 525 drive so we can check on Ethernet comms. Is there a parameter we can toggle that will give us feed back letting us know that we are communicating with the drive?
  Reply With Quote
Old November 21st, 2020, 04:27 PM   #2
Phrog30
Member
United States

Phrog30 is offline
 
Join Date: Dec 2006
Location: Montgomery, Alabama
Posts: 721
Search GSV entry status. Many examples and help. The drive will automatically stop on loss of comms by the way.
  Reply With Quote
Old November 21st, 2020, 04:34 PM   #3
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 351
Quote:
Originally Posted by Phrog30 View Post
Search GSV entry status. Many examples and help. The drive will automatically stop on loss of comms by the way.
If configured that way, and I believe that is the default. There are parameters that will allow the drive to operate in various states after a net loss.
  Reply With Quote
Old November 22nd, 2020, 02:16 AM   #4
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 364
Quote:
Originally Posted by RY_Guthrie View Post
We are trying to set up a watch dog for a rockwell 525 drive so we can check on Ethernet comms. Is there a parameter we can toggle that will give us feed back letting us know that we are communicating with the drive?
I think the easiest way is for you to monitor the "Connection.Faulted" bit or "Fault" DWORD, or whatever is in the profile for the device that indicates the communication status, which is mapped directly onto the controller tags "I" file for the particular device. The below screens I hope is clearer than my explanation.
Attached Images
File Type: jpg 20201122_EIP_CommsSts.jpg (190.1 KB, 82 views)
  Reply With Quote
Old November 22nd, 2020, 09:27 AM   #5
Phrog30
Member
United States

Phrog30 is offline
 
Join Date: Dec 2006
Location: Montgomery, Alabama
Posts: 721
Quote:
Originally Posted by AlfredoQuintero View Post
I think the easiest way is for you to monitor the "Connection.Faulted" bit or "Fault" DWORD, or whatever is in the profile for the device that indicates the communication status, which is mapped directly onto the controller tags "I" file for the particular device. The below screens I hope is clearer than my explanation.
You assume wrong if you think all IO has this option. Add a PF525 in your tree, there is no connection status. You will need to use a GSV. This option is better anyways because you will get the actual status, running, faulted, configuring, etc.
  Reply With Quote
Old November 22nd, 2020, 06:57 PM   #6
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 364
Quote:
Originally Posted by Phrog30 View Post
You assume wrong if you think all IO has this option. Add a PF525 in your tree, there is no connection status. You will need to use a GSV. This option is better anyways because you will get the actual status, running, faulted, configuring, etc.
Thanks for pointing out my wrong assumption. I did not know devices such as PF525 did not support such feature.
  Reply With Quote
Old November 24th, 2020, 10:19 AM   #7
jdbrandt
Lifetime Supporting Member
United States

jdbrandt is offline
 
jdbrandt's Avatar
 
Join Date: Oct 2002
Location: Pennsylvania
Posts: 1,111
Quote:
Originally Posted by RY_Guthrie View Post
We are trying to set up a watch dog for a rockwell 525 drive so we can check on Ethernet comms. Is there a parameter we can toggle that will give us feed back letting us know that we are communicating with the drive?
If the on-board I/O is not assigned, you could attach an unused output (the relay) to any unused input, and then use your program to turn the relay ON, and OFF, at a slow rate. The input should follow...and if it does not, you have a communications problem.

GSV is easier.
__________________
Jeffrey D.Brandt
  Reply With Quote
Old November 24th, 2020, 12:30 PM   #8
Chuck Woodbury
Member
United States

Chuck Woodbury is offline
 
Chuck Woodbury's Avatar
 
Join Date: Apr 2005
Location: Valley Springs, California
Posts: 70
In the GSV use Class Name "Module" Instance Name is your drive from your IO Tree, Attribute is Entry Status and put it to a Integer destination of your choosing. Then use a BTD, Bit 12 of the last integer, move it to a new Connect Status integer at bit 0. As long as the value of the Connect Status is 4, comms are good.
__________________
A common mistake that people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools. - Douglas Adams
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Allen Bradley 525 Drive Current Settings fredjohns LIVE PLC Questions And Answers 5 August 7th, 2019 02:17 PM
allen bradely 525 drive trouble mavrick LIVE PLC Questions And Answers 16 May 24th, 2019 01:07 PM
525 Multi Drive Explicit Messaging ControlP LIVE PLC Questions And Answers 1 December 12th, 2014 03:02 PM
Power Flex, Drive Logix and Control Logix Tim LIVE PLC Questions And Answers 2 January 4th, 2007 06:37 PM
AB MO2AE & Yaskawa SGM drive kenschunk LIVE PLC Questions And Answers 1 September 23rd, 2006 08:25 PM


All times are GMT -5. The time now is 06:49 AM.


.