Old November 17th, 2020, 05:39 AM   #16
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by Peter Nachtwey View Post
...a big valve that had a 12 inch stroke....

Hooah! I haven't seen one of those up close in a few decades.
  Reply With Quote
Old November 17th, 2020, 06:57 AM   #17
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,261
I think... MarkT is going to leave us hanging and we are never going to get our questions answered, I still think if this is a new system the designer of the system needs to be involved, there are way to many variables that will need to be addressed before you could even start on the PID tuning
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old November 17th, 2020, 10:59 AM   #18
drbitboy
Lifetime Supporting Member
United States

drbitboy is offline
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 1,655
Quote:
Originally Posted by geniusintraining View Post
...if this is a new system...

Good point, if this is a commissioning, by now the OP may have even forgotten they asked a question here.


And this is the first time they attempt to tune a PID? Oh dear.
  Reply With Quote
Old November 17th, 2020, 11:49 AM   #19
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,261
Quote:
Originally Posted by drbitboy View Post

And this is the first time they attempt to tune a PID? Oh dear.
We all remember the 'first times'....

I was reheating a thermal oil system, because it was old and had so many additions it was a water boiler to heat exchanger, to oil, back to water, the hot water tank was just over 100k gallons and ran about 500 deg f and was about 16 bar pressure ran good until you had to cool the system down and work on it... I about cried when they told me to reheat the system (everytime), you would start at the boiler and work your way up, the banging of the pipes would scare the living **** out of you, all I could think of was that hot water tank blowing up, I did make one of the heat exchanges jump about 6 inches but the worst was.... when we got a leak in the oil system and the water leak in once the water would hit a hot side and steam off it would be like a small explosion but when you saw a pressure gage go from 2 bar to 20 (max) in less than a millisecond
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old November 17th, 2020, 11:56 AM   #20
NetNathan
Lifetime Supporting Member
United States

NetNathan is online now
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,792
Being from the heat treat industry, I hate tuning Heat/Cool PIDs. Tuning can be a big issue due to performance of the type of heating device and the cooling device.
There are temp controllers that handle Heat/Cool PIDs rather well.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old November 17th, 2020, 12:35 PM   #21
padees
Member
United States

padees is offline
 
padees's Avatar
 
Join Date: Aug 2011
Location: Michigan
Posts: 659
1746-BTM... add whatever comments you like.


It could be interesting...
  Reply With Quote
Old November 17th, 2020, 01:43 PM   #22
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 7,269
Quote:
Originally Posted by NetNathan View Post
There are temp controllers that handle Heat/Cool PIDs rather well.
yes! We have a thermal chamber for heat stressing boards. The control is made by Watlow. We need to test boards from 0 to 70 degrees C do the controller must heat or cool.


However, I don't think that is the main issue. The OPs system is much more complicated than a simple thermal chamber. I still haven't found out of there is feedback from the valve spool position.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 18th, 2020, 03:22 PM   #23
grnick50
Lifetime Supporting Member
Greece

grnick50 is offline
 
Join Date: Nov 2010
Location: Ptolemaida
Posts: 332
I know you are using AB but here is link for an example from Siemens. You can examine the principles and maybe you can find useful info.

https://support.industry.siemens.com...dti=0&lc=en-AR
  Reply With Quote
Old November 18th, 2020, 06:10 PM   #24
mark.t
Member
United States

mark.t is offline
 
Join Date: Feb 2015
Location: USA
Posts: 6
Peter,
Yes, both valves are actuated with air.
  Reply With Quote
Old November 18th, 2020, 06:45 PM   #25
mark.t
Member
United States

mark.t is offline
 
Join Date: Feb 2015
Location: USA
Posts: 6
Guys,
Sorry I have not been able to answer quickly. I attend college and have been extremely busy. With that said, the system is a new installation and works perfectly in manual mode, I can actuate my valves 0 to 100% in response to 4-20mA (both heating and cooling without any issues). The problem is strictly PID control. I did a step test a few days ago and using the Ziegler Nichols formula calculated the values for tuning which ended up giving me a very sluggish response when I tested today. The PID slowly creep up and down, thus overshooting. The system uses two jackets in series and is set for heating only (steam) or cooling only (chilled water) at a time, that is why I need the critical damping. The process is monitored by an RTD at the bottom of the tank. The PID is set to Dependent, not sure if switching to independent may help to achieve better control. I got with Rockwell for training, but due to COVID that class is on hold for now.
  Reply With Quote
Old November 19th, 2020, 01:49 AM   #26
PLCnovice61
Member
Australia

PLCnovice61 is offline
 
Join Date: Apr 2015
Location: home
Posts: 291
mark.t, l will re-ask Peters question, do you have feed back on your valves, in other words how do you know if the valves have gone to the desired settings?
  Reply With Quote
Old November 19th, 2020, 09:56 PM   #27
mark.t
Member
United States

mark.t is offline
 
Join Date: Feb 2015
Location: USA
Posts: 6
Quote:
Originally Posted by PLCnovice61 View Post
mark.t, l will re-ask Peters question, do you have feed back on your valves, in other words how do you know if the valves have gone to the desired settings?
The valve has a digital display that shows the percent open at any given time and also a mechanical indicator at the stem. Have not been able to do any further tuning. I will give it a shot next week again with maybe P and D only settings to see how it goes and also do a few more bump tests for repeatability of dynamics.
  Reply With Quote
Old November 19th, 2020, 11:23 PM   #28
PLCnovice61
Member
Australia

PLCnovice61 is offline
 
Join Date: Apr 2015
Location: home
Posts: 291
mark.t, does the valve give feed back to the PLC, showing % on the display isn't going to help the PID
  Reply With Quote
Old November 20th, 2020, 01:39 AM   #29
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, US
Posts: 7,269
I feel like this
Attached Images
File Type: jpg pt1.jpg (21.7 KB, 106 views)
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 20th, 2020, 11:53 AM   #30
maperry98
Member
United States

maperry98 is offline
 
Join Date: Nov 2020
Location: Muncie
Posts: 9
You can have the PLC change the PID settings when the temperature gets 15 degrees from the setpoint. Look at the Logix help section for the PID instruction for the name of the setting you want to change. For example, the Control Variable Minimum will be .MINCV and the Control Variable Maximum will be .MAXCV. You can use a MOV instruction to change the values back and forth to get the PID to do what you need it to do.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Quick comparison of PID, PIDE, and PI instructions in RSLogix5000 ... Ron Beaufort LIVE PLC Questions And Answers 14 June 7th, 2018 02:24 PM
PID for MicroLogix 1500 - conversion issues ... Ron Beaufort LIVE PLC Questions And Answers 5 November 8th, 2005 10:03 AM
learning PID for Allen-Bradley ... Ron Beaufort LIVE PLC Questions And Answers 9 August 23rd, 2005 02:40 PM
AB PLC5 PIDs Derek McFarland LIVE PLC Questions And Answers 23 March 2nd, 2005 02:18 AM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 11:57 AM


All times are GMT -5. The time now is 02:29 PM.


.