Dear Friends
I needs your help , Please Is necessary to copy all S7 Program in both PLC , Master & Slave or only in Rack-0- PLC ?
Best Regards
Ali
Many Thanks fredz0003 , My point as below and attached pic.
Master CPU have "S7-Program & Connections" under their tree
Slave CPU have only "Connections " under their tree
Is that normal for Redundant works
Yes, is normal. Two H cpus form a single station. The PG uses one program only. when you transfer the program will be loaded in both.
Yes it is normal. However @rjua mentioned when you transfer it loads on both CPU's. In my experience when I've downloaded projects to both CPU's you have to download one at a time.
I could be wrong maybe other projects are setup different, but that's just my experience.