Redlion DataStation Plus to Multiple PLCS (Omron) 1 Ethernet Line

Tommycai

Member
Join Date
Aug 2011
Location
KY
Posts
120
I am having a problem with communication Ethernet /Ip. The relay time in transmitting information is roughly 6 seconds
From PLC to redlion to server running php and back to plc

We have 6 CJ2M PLCs going to a switch and the switch going to a redlion. The switch is managed also. Any ideas would be appreciated.
 
If anyone needs to use this later on. the fix seems to be change the UDP Port #'s for each plc you have to match up and make no 2plcs the same udp port
 
If anyone needs to use this later on. the fix seems to be change the UDP Port #'s for each plc you have to match up and make no 2plcs the same udp port

Did you try this with multiple Ports? In other words, putting each PLC on a Separate Network Protocol (there are 4 of these by default). This is limited to 4 on a DSPLE, but you can have up to 10 on a DSPSX.

If you did it this way, I wouldn't think you would need to change the UDP Port.
 

Similar Topics

Hi, I want to make a schedule with redlion datastation plus, but i dont see how. I need to have a web page were i insert the start time, run...
Replies
1
Views
1,893
On my DSP, I’ve been experiencing a strange and repeatable event. When viewing the HMI screen via the webserver, the device resets when...
Replies
5
Views
3,342
Does anyone know if the Red Lion Datastation range can do Profinet? Basically we have a machine with a PN/PN coupler serving the data we need...
Replies
5
Views
1,925
I have a RedLion datastation logging data to a CF card. When i disconnected the PLC, it seems to keep logging the last read data. Is there a way...
Replies
4
Views
2,056
Hey guys, hoping someone here could give me a little advice. I'm working with a CR1000-04000 in Crimson 3.1 and I was interested in adding the...
Replies
4
Views
114
Back
Top Bottom