140 CPU11303 Modicon Quantum

Have you removed the CPU batery?

If yes then i think the cpu have lost its program and also comms port setup.

So possibly the cpu is blank and may need re-configuring.


Check the comms port settings in proworx project are set correctly, check parity, stop bits, data bits etc. Set to the same as the USB or comms port on your laptop.

I am recalling this from memory its been a while since i used proworx 32. So may not be accurate.
 
Thanks Mr.cookie
Exactly same as your text ( talk)
I did removed power then changed battery.
Program on the CPU deleted.
I will try to reprogram ( download backup program).
I did check and setting all functions: baud rate, stop bit, parity, data bit, to default settings ,
Both same as on computer and PROWORX32.
Ok .proworx32 can found the CPU on the network explorer, but appear: ( Busy Controller ) , so that can't to downloaded program.

I contacted to Schneider Customer, they told me connect with CPU by
(UNITY PRO )

What is this hell!?
Price of Unity pro : $2000 to $20,000
 

Similar Topics

Anyone can instruct or has manual on how to connect to 140 CPU 113 03 via Concept XL 2.6 to upload program backup ? and which connection mode to...
Replies
0
Views
599
Hi, First of all, thanks in advance for those who support and advises. I have a Modbus/TCP operational network as shown below. However, at any...
Replies
0
Views
909
Hi, I have a Modbus/TCP operational network. Last week a NOE 771 01 on one of my Hot Standby PLC System, Standby PLC stopped communicating. On...
Replies
1
Views
1,883
I need to get connected to an older machine that has been in storage for years. It utilizes a Scheider Electric 140 CPU 434 12A. I have not...
Replies
3
Views
2,672
i have problem about GE PLC VersaMax ic200udr140 It has been set to ip connection But i do not know ip How i want to initialize it?
Replies
1
Views
2,423
Back
Top Bottom