S7 v5.6 4-20ma scaling issue

My bad. I dint read all the posts.

Well you simply cannot use the Siemens FC105 for a Wago analog input. The scaling does not fit.
Siemens FC105 assumes 0-27648
Wago 750-455 is 0-32760
Making a custom scaling block is easy.
 