New to the site. I am trying to meassge between a Compactlogix 1769-L18ER-B1BB and a Micrologix 1400.

I am using Studio 5000 V24. I can find plenty of videos giving instructions on how to do this . However, when I get to the "Communication" portion of the MSG instruction I cannot see my Micrologix and manually inputting the IP doesnt work either. If I try to add the ML 1400 as a new module in the control organizer I cannot see it there either. I can however ping the ML as well as see it in RSLINX. Any help would be appreciated.

One last note. If I try to add the ML 1400 as a module it is also not listed in the "Catalog" section to be selected as a module type.
 
The MicroLogix 1400's (and 1100's for that matter) don't support EtherNet/IP CIP, only PCCC so it won't show up in the IO tree nor will be be a module in the "catalog". You need to use a "SLC Type Read" or "SLC Type Write" in the "Message Type" when setting up your message instruction in the CompactLogix. There are two basic types of EtherNet/IP, CIP and PCCC and they are not compatible with each other. The MicroLogix only supports PCCC (as does a SLC5/05) however the CompactLogix will support both which is why you need to tell it to use PCCC (that's what setting up a "SLC Type Read/Write does). Do another google/YouTube search for messaging between a CompactLogix and a MicroLogix (not to be confused with Micro 800's).
 

Similar Topics

I have a master PLC in CompactLogix and multiple slave PLCs in MicroLogix. The master is writing a value to the slaves, but in case of comm loss...
Replies
2
Views
1,866
Anybody have some tips on getting a CompactLogix 533ER to allow messaging with a MicroLogix 1100? Set the CompactLogix up with the 2...
Replies
0
Views
2,350
All, I'm working on a communication project between 2 departments. I have a PV Plus 1250 in one department on a Micrologix 1100 (RSLogix 500)...
Replies
0
Views
2,300
I wanted to double check something, and make sure I'm not just overlooking an obvious solution. I have a system that will be running an L35E...
Replies
3
Views
4,079
Hi all I'm trying to setup a MSG connection (which I'm not familiar to) between a CompactLogix CPU (L310ER) and a Micrologix 1400 CPU. At the...
Replies
1
Views
807
Back
Top Bottom