Communication-Signal transmission -1.5kM - Better option

Selk

Member
Join Date
Aug 2019
Location
Dammam
Posts
2
I am looking for a method which transmit OPEN/CLOSE signal from "A" Pump Station to "B" Pump Station.

(a) There is no wire connection between two Pump Stations, 1.5km apart.
(b) Ordinary wireless device is prohibited to use.
(c) Mobile telephones work at both Pump Stations.
(d) Internet service is not available at both Pump Stations, but probably set up newly if required.

Thank you!
 
Is there a PLC or RTU capable of communications at both ends? If so, using a radio modem to set up communications is one option. For 1.5km you might be able to use the Schneider Trio JR900 series licence free model, depends on local obstructions and radio spectrum licensing in your country.

If thats a bit over kill, take a look at Elpro wireless I/O
 

Similar Topics

Hello folks, Hope everyone is doing well. I am a beginner at working in analog signals with PLC Analog module: 1769-IF4 ( 4 analog inputs ) PLC...
Replies
9
Views
1,353
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
133
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
64
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
73
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
150
Back
Top Bottom