I/o Not Responding

chan0828

Member
Join Date
May 2008
Location
ontario
Posts
6
I am working on Allen Bradely PLC 5000 (RSLogix 5000).
If I see "I/O not responding" blinking (green light), what can cause this happen? Please answer me with all possibility even extremely low possibility.
Thanks.
 
The most common reason, is the processor has a communications module configured in the I/O configuration tree, that has no actual I/O attached.

Most commonly, would be an Ethernet module. If it's only there for comms, it should not be in the I/O tree. Other comms gateway modules can do the same, DHRIO, CNB, anything that doesn't actually have physical I/O on it.
 
rdrast has it, but while online with the PLC look in the I/O tree, the offending module should have a yellow triangle over it.
 
i/o not responding error

Have 5 1756-L72S GuardLogix 5570 Safety Controllers on independent machines in one room. Using Stratix wireless access points. Wanting to produce/consume bits back and forth.
1. Do I add the other PLCs under the WAP on the I/O tree?
2. I have added the other PLCs under the EN2T module, but I get intermittent I/O Not Responding Error.
3. I can pass a bit back and forth, but not reliably and with various delay.

What should I try please?
 
wireless access points. Wanting to produce/consume bits back and forth.

Go find whomever told you this was a good idea.

Slap them in the face.

The come back and create another thread that describes exactly your switch and wireless architecture and folks might be able to suggest some configuration and troubleshooting tips.

Edit: I'm kidding, a little. Wireless is notorious for dropping packets and being unreliable. The first thing you have to do is find out if your wireless system is carrying floods of safety or I/O data that it doesn't have to, and that's going to take some protocol analysis. We should first decouple it from this fossilized thread and consider the technologies and techniques from a fresh start.
 
Produce/Consume wirelessly generally isn’t a good idea as Ken was not so subtly alluding to. However it might be possible to reduce the number of dropouts (and even maybe eliminate them all together) by increasing the RPI’s for the consumed tag. I’d change it (the RPI) to as long as possible and as long as the application will tolerate. Having said that given that it’s a safety controller that might not be a good idea and you might be looking at getting all of the needed equipment onto a LAN (hard wired).
 

Similar Topics

hello, I have a Maple Systems HMI5103L currently programed and running in conjunction with a AB 2080-LC50-24QWB. everything works fine data is...
Replies
2
Views
717
Have tried to get the tag details from the PLC through python pycomm module.But getting Tag doesn't exist error. Am using pycomm version = 0.11.0...
Replies
1
Views
508
Hi everyone. I worked with RedLion HMI several years, in the last year four CR3000 HMI (10 and 15") had have problems with the touchscreen. All...
Replies
5
Views
1,253
some of the existing ethernet IO modules having problems after adding couple camera(Keyence IV3).Tried swapping the switch with a bigger one...
Replies
5
Views
1,636
Hi every one am working on this machine ,where there is a motor that rotates an arm with high speed when the arm reaches the sensor the motor...
Replies
8
Views
2,002
Back
Top Bottom